Hello all,

I have a dreaded Halstead Ace High boiler. I've become pretty familiar with it over the years following a necessary service to the diverter valve and diaphragm. It's developed a new issue though which has me stumped:

When a demand is created via a tap: the DHW Flow switch is pushed, the pump starts, the primary flow switch engages and as soon as that happens it just cuts out. No warning light, no overheat trigger, it just stops dead. I can only repeat this by turning off and on again. There absolutely no response to a CH demand and I have to restart it to get any other response at all.

This isn't a PCB issue, I have tried several new PCBs for each exhibits the same behaviour. Could it be something related to the Thermistors or APS?

I would be most grateful for any suggestions, it's getting very cold indeed.
 
Your best option would be to phone a local gas safe engy up and get them out
 
We cannot give out advice relating to gas repairs on the forum for saftey reasons a gas safe engineer is needed . sorry kop
 
Hello all,

I have a dreaded Halstead Ace High boiler. I've become pretty familiar with it over the years following a necessary service to the diverter valve and diaphragm. It's developed a new issue though which has me stumped:

When a demand is created via a tap: the DHW Flow switch is pushed, the pump starts, the primary flow switch engages and as soon as that happens it just cuts out. No warning light, no overheat trigger, it just stops dead. I can only repeat this by turning off and on again. There absolutely no response to a CH demand and I have to restart it to get any other response at all.

This isn't a PCB issue, I have tried several new PCBs for each exhibits the same behaviour. Could it be something related to the Thermistors or APS?

I would be most grateful for any suggestions, it's getting very cold indeed.

Hello Dan,
I have the same boiler and had a similar problem, seemed to be no logical answer.
 
Last edited by a moderator:
Hello Dan,
I have the same boiler and had a similar problem, seemed to be no logical answer.

Most logical remedy with these Halsted boilers is to replace them, parts are to expensive, and Glen Dimplex don't want to know, but like charging premium rates on Tec phone line
 
I understand about the gas safety stuff and appreciate you guys doing your due diligence. I'm certainly not touching anything gas related, the general consensus is just to get rid of the thing which I am to do as soon as possible. For the record I replaced the thermistors and it did nothing so back to the drawing board... Or the Worcester catalogue!
 
Status
Not open for further replies.

Reply to Halstead Ace High (DHW+CH) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

M
Hi, Hopefully someone can throw some light on if this is a real issue or not. I have had this boiler for about 10 years, I noticed just recently...
Replies
1
Views
421
Hi, As per the thread title, I have an Ideal Logic Combi 30 and I am having a problem with the pump, which keeps activating without any DHW/DCH...
Replies
2
Views
1K
Halstead ACE HE30 combi boiler dhw issue, intermittent no hot water worse when heating been on. replaced hydroblock, diverter actuator, pcb and...
Replies
7
Views
2K
80e works 90 per cent well. But when running shower, intermittently stops heating and restarts. It's not the DHW temp sensor. I don't think the...
Replies
0
Views
657
Hello All- (Usual caveats apply: I am the rather unusual part-time variety of a GSRE, training self-funded and slowly trying to make my way and...
Replies
0
Views
66
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock