Carrera

Hi, i am looking for advice regarding my system. The plumber/heating engineers have been going round in circles trying different things and I am not sure they're will get to a solution.

The issues -
1. When the underfloor heating is on, the hot water cylinder does not heat up.
2. When heating just the hot water cylinder, the boiler starts cycling heavily.
3. Underfloor heating individual loops, flow rates drop as more manifolds come online.

The system -
Worcester Bosch 40cdi conventional, grundfos Magna 1 pump, Ariston 500 litre hot water cylinder, all located in a basement plant room. There are 6 underfloor heating manifolds, with ports varying from 6 to 10 with differing loop lengths, arranged over 4 floors. The system is controlled via a heatmiser network system with 30 stats in each room. There is also a towel radiator curcuit with 6 rads which we have not yet bought into the combined running equation yet.

The flow out of the boiler goes to the pump, then up to the two feeds to the manifolds ( First feed to 3 manifolds on one side of the house, ground floor, first floor and attic floor, second feed to 2 other manifolds ground floor and first floor and a third feed to the towel rad circuit). Before these feeds there is a T which feeds the hot water cylinder and the final manifold in the basement.

Temperatures at the manifolds in consistent at about 42c and the holier is outputting at 71c.

All zone valves operate correctly, all stats and timers are running and wired correctly.

Heat loss calcis have been done to size the boiler to the heat output required, indicating the boiler is oversized by about 8kw. The system has been in for about a year and it took us a while to figure out why the water was not heating properly.

Effectively when the heating is on the flow does not go through the T to the cylinder, but when the heating is off it does and therefore heats up the water.

Things that have been tried - pump has been upgraded to the one now in place, pipe work taken apart an equivalent of a low loss header using loops and spaced Ts has been tried and then removed. The T has been turned around to reduce resistance.

Any help or advice would be really appreciated as this is driving me nuts.
If I have missed vital information please let me know and I will try and answer.
many thanks in advance.
 
sounds like you need some balancing valves is the basement manifold of the same feed as the cylinder ? have you tried it with that manifold isolated
 
If a low loss header was fitted, why wasn't the cylinder piped back to this with its own circulator ? This would have cured it .
 
No heating of cylinder when underfloor is on? Just an idea, but is the flow temp from the boiler staying high even with all the underfloor calling? The only reason I say this is that I've had a situation like this in the past, and found that if the return coming back from the underfloor is very cold and the boiler can't put enough heat into the water in one pass to raise it to the temperature required for hot water preparation then it can cause similar symptoms. Checked volume/mass flow rate through the boiler and had a look at what the flow and return temps are doing? this doesn't answer the hot water cycling issue though.I guess if this was the case, the solution would be to implement some form of hot water priority set up. Like I say, just an idea.
 
Thanks for the replies so far, responses:

Stevetheplumber
Basement manifold is off the same feed as the cylinder
if I isolate the basement manifold and just run that, hot water and basement heating work together, as soon as I switch the rest on I loose the hot water cylinder and basement manifold

Chalked
re the low Loss header and and circ back, I will talk to the plumber

Bennygas
re temp being very on return, even if one manifold is running, ie low heat call I still get nothing flowing through the cylinder
 
Hi Carrera -

Welcome to UKPF - you in the right ball park for help - I have read your post
carefully and have some observations and questions.

1. Do you own a porsche motor car - if which model
2.the specifcation you present of your c/h system is top dollar - it has been well designed

so- I think the problem is in the fitting or most likely a component - as it is so new
can you get the installer back ? - my outfit would rtn to problem like this even if is
beyond our promise

3. To help us can you post a diagram of your set up then we can all have a look

Centralheatking
 
Hi centralheatking,
1 don't own a porsche I wish I did, but all funds have gone into self build.
the installer designed the system,Manx they are in trying to sort it out but going round in circles trying things. I thought I would try and get some fresh views to help as I have to switch between heating and hot water manually at the moment, not what I was expecting.
i will try and put a drawing together of the plant room, but may be easier to take a picture and post it with some annotations. Would that help?
Regards
 
Things that have been tried - pump has been upgraded to the one now in place, pipe work taken apart an equivalent of a low loss header using loops and spaced Ts has been tried and then removed. The T has been turned around to reduce resistance.

Any help or advice would be really appreciated as this is driving me nuts.
If I have missed vital information please let me know and I will try and answer.
many thanks in advance.
Has there ever been more than one pump on the system ??
You say the original one was upgrades to the Magna but for a LL system to work there must be a constant flow rate through the boiler (as required by the boiler manufacturer) so a dedicated circulator would be required for this & than as a minimum a circulator for the HWS primaries & one for the heating.
Without the required flow rate the temp at the boiler quickly rises & it modulates down.
 
Has there ever been more than one pump on the system ??
You say the original one was upgrades to the Magna but for a LL system to work there must be a constant flow rate through the boiler (as required by the boiler manufacturer) so a dedicated circulator would be required for this & than as a minimum a circulator for the HWS primaries & one for the heating.
Without the required flow rate the temp at the boiler quickly rises & it modulates down.


Originally one pump, then LL SYSTEM had 3 pumps, one circulating, one feeding heating demand, and one trying to pump round the cylinder (unsuccessful), now back to one pump but a bigger one
 
I thought would be easier to put in a picture of the plant room rather than a sketch, but having trouble up loading it using the insert picture button. is there a trick to it?
 
I would suggest electrical fault, sounds like the hot water circuit isn't opening when the rest is open. If it all works individually then it is all working but not as it should, either this or a balancing issue. My guess would be an electrical fault though. Possibly one of the 2 port valves not wired correctly
 
If you get ufh up to temp I .e house is at 25 c then lower set points on ufh with cylinder in demand and cyl should heat up if electrical system in correctly. Sounds more like the return from one of the blended returns ( ufh) is running through cylinder ? Balancing / hydraulic issue.

Which cylinder cold switch on hw load . Run until flow is hot , ( run off hot water to ensure demand in cylinder is constant)
Turn on one manifold at a time and wait until the return is at a constant temp, keep working through until you switch one on and cyl flow goes cold. Then you know which one is the prob.
 
image.jpg
Don it albeit sideways!
this is the plant room setup
 
Presumed the cylinder was miles away.! Problem that sticks out to me is why is there a tee off before the pump?
pressure vessel?
another pump? Noooo
 
Is that a two or 3 port on cyl? Where do the pipes at bottom on pic disappear to?
Yes the tee under the boiler behind pump also interesting? What's the total load on the heating system as it looks to be 28 and 22 mm
 
The house has underfloor throughout so output may be ok.
I personally think wb heat exchangers are too restrictive.
a house of this size would have been better served with two smaller boilers on a low loss header. As underfloor does not need a lot of kw, but needs a good flow rate.
 
Is that a two or 3 port on cyl? Where do the pipes at bottom on pic disappear to?
Yes the tee under the boiler behind pump also interesting? What's the total load on the heating system as it looks to be 28 and 22 mm
Zooming in its a zone valve.
 
The house has underfloor throughout so output may be ok.
I personally think wb heat exchangers are too restrictive.
a house of this size would have been better served with two smaller boilers on a low loss header. As underfloor does not need a lot of kw, but needs a good flow rate.

6500sqfoot house
6 manifolds 500litre unvented cylinder
Inch pipe all to small for my liking
 
The house has underfloor throughout so output may be ok.
I personally think wb heat exchangers are too restrictive.
a house of this size would have been better served with two smaller boilers on a low loss header. As underfloor does not need a lot of kw, but needs a good flow rate.

Yes but if cylinder is asking for 18kw and ufh is asking for 15kw possible issue?
 
Quick calc for underfloor ( not exact or knowing the property)

1600 square feet = 603-87 m square.

solid floor at 21*c. Works out at roughly 37 kw! Boiler undersized.!


all this does not cure the problem with the cylinder though.
 
A low loss header would of been good for that set up
But to be honest I would be thinking the plumber made a hash of that as pipework is undersized
Another good job ruined by cutting corners imho
 
A low loss header would of been good for that set up
But to be honest I would be thinking the plumber made a hash of that as pipework is undersized
Another good job ruined by cutting corners imho

Boiler is a 1/3 of the size it should be ? 604m2 @0.150kw/m2 = 90kw just for the floors! 90kw ain't ever fitting down 28mm unless it's running at 140m/s
 
Status
Not open for further replies.

Reply to Advice needed. Issues with underfloor heating and hot water system for new build in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
282
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
224
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
122
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
453
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
324
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock