Search the forum,

Discuss Unvented cylinder problems - over pressure or faulty expansion tank? in the USA area at PlumbersForums.net

Messages
1
Hi,
New to this forum and also complete novice who knows pretty much nothing about plumbing.
However I have done quite some google searching trying to find some answers.
I live in a 1st floor flat which uses an electric duel element direct unvented water heater cylinder (150 litres).
Recently I noticed a small leak somewhere on the copper pipe with the pressure relief valve and tundish. But I think its been leaking for some time because there is green corrosion and scale all down the copper pipe, and also lots around where the valve outlet connects to the tundish.
I have also seen a lot of water running through the tundish in the mornings when the waters being heated, which according to my searches, means either the pressure valve is faulty (which going by the corrosion I mentioned, could be?), or there is actually too much pressure perhaps because of a faulty expansion tank.
The pressure valve red cap says rated for 7 bar, is this normal? All mentions I could see of such devices were around 2-3 bar.
Currently got a bucket under where the drips are forming, collecting about 2 inches a day.
 

Attachments

  • 248226520_433998408125347_398880280970202392_n.jpg
    248226520_433998408125347_398880280970202392_n.jpg
    60.4 KB · Views: 42
  • 254966018_944176349833944_3264047903734689738_n.jpg
    254966018_944176349833944_3264047903734689738_n.jpg
    99.6 KB · Views: 37
  • 255546971_612886626533079_4313913707149330647_n.jpg
    255546971_612886626533079_4313913707149330647_n.jpg
    63.7 KB · Views: 33
  • 255583682_312409853742753_2691217238652746760_n.jpg
    255583682_312409853742753_2691217238652746760_n.jpg
    80.9 KB · Views: 45
You will need a service call that expansion vessel looks as though it's not supported at all when these fail they are really heavy and will cause problems if not secured , the pressure relief will need changing and all other safety devices need checking . Kop
 
Your system has lost its expansion capability. The problem is due to the expansion vessel having lost its air charge and results from either an air leak to atmosphere or a failed diaphragm.
You would need to depressurise the hot water system by shutting off the cold feed and then opening a hot tap. If the expansion vessel is healthy then water should come out of the tap for quite a few seconds before stopping. If it 'dies' straight away this is a sign of the expansion vessel being full of water due to losing its charge. Most vessels have a simple tyre type valve/connector under the plastic cover and with the system depressurised there should be an internal pressure of say 1 Barg. This can be checked using a tyre pressure gauge. If there is no residual pressure to unit is faulty. Quickest solution go the plumbers merchant and buy a new one. set the pressure to 1.0 Barg using a tyre pump and refill your system the mains water pressure will do the rest.
 
Hi,
New to this forum and also complete novice who knows pretty much nothing about plumbing.
However I have done quite some google searching trying to find some answers.
I live in a 1st floor flat which uses an electric duel element direct unvented water heater cylinder (150 litres).
Recently I noticed a small leak somewhere on the copper pipe with the pressure relief valve and tundish. But I think its been leaking for some time because there is green corrosion and scale all down the copper pipe, and also lots around where the valve outlet connects to the tundish.
I have also seen a lot of water running through the tundish in the mornings when the waters being heated, which according to my searches, means either the pressure valve is faulty (which going by the corrosion I mentioned, could be?), or there is actually too much pressure perhaps because of a faulty expansion tank.
The pressure valve red cap says rated for 7 bar, is this normal? All mentions I could see of such devices were around 2-3 bar.
Currently got a bucket under where the drips are forming, collecting about 2 inches a day.
Ignore the post from Pete above ^^^^^^ hes guessing. You need an experienced G3 man .
 
Your system has lost its expansion capability. The problem is due to the expansion vessel having lost its air charge and results from either an air leak to atmosphere or a failed diaphragm.
You would need to depressurise the hot water system by shutting off the cold feed and then opening a hot tap. If the expansion vessel is healthy then water should come out of the tap for quite a few seconds before stopping. If it 'dies' straight away this is a sign of the expansion vessel being full of water due to losing its charge. Most vessels have a simple tyre type valve/connector under the plastic cover and with the system depressurised there should be an internal pressure of say 1 Barg. This can be checked using a tyre pressure gauge. If there is no residual pressure to unit is faulty. Quickest solution go the plumbers merchant and buy a new one. set the pressure to 1.0 Barg using a tyre pump and refill your system the mains water pressure will do the rest.
This is not strictly true Pete your giving the advice for a heating expansion vessel that is set at 0.7 - 1 bar ? . A potable expansion vessel is not something a DIYer should be changing it needs replacing and supporting correctly and should be fitted with a flow through valve the new vessel is set at 0.2 below the incoming water supply pressure this avoids water hammer , contamination and protects against legionnaires disease , the cylinders combination valve filter will need cleaning and the safety devices checked and replaced if found to be faulty again this is not something a homeowner should be attempting , these problems are normally due to the lack of maintenance and servicing and the COVID epidemic has seen people leave important safety checks, as a consequence their systems are failing and are costly to repair or replace. Regards kop
 

Attachments

  • Screenshot_20211113-045847.png
    Screenshot_20211113-045847.png
    319.4 KB · Views: 21
  • Screenshot_20211113-050028.png
    Screenshot_20211113-050028.png
    189.3 KB · Views: 21
  • PXL_20210319_085445639.jpg
    PXL_20210319_085445639.jpg
    287.4 KB · Views: 19
Last edited:

Reply to Unvented cylinder problems - over pressure or faulty expansion tank? in the USA area at PlumbersForums.net

Similar plumbing topics

I have done pressure test for 2" high pressure pipe line by closing the pipe with rubber plugs at the ends. It was 3 bar and I kept it for 24 hours. Its shows a pressure drop of 0.5 bar. The pipe line is fully exposed and I couldn't find any leak on them. What might be the problem. If somebody...
Replies
5
Views
193
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
376
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
161
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...