Matt0029

Gas Engineer
Messages
1,137
I was at a job today and notice a 7litre under sink heater was fitted. Because of the size under 10litres do these not need a pressure relief valve and expansion vessl? It didn't have any of the kind. Thanks.
 
Yes they do require them
 
Doesn't all unvented regardless of how small require both? With no expansion vessel the pressure will rocket when heated
You can put a loop in the cold water pipe work between the check valve and the unit I think and is an acceptable way of not having an expansion vessle, I seem to remember?
[automerge]1578340624[/automerge]
You can put a loop in the cold water pipe work between the check valve and the unit I think and is an acceptable way of not having an expansion vessle, I seem to remember?
Though there isn't even that on this one
 
As you know when water is heated its average kinetic energy rises. Molecules move faster and if no room for expansion they bounce of system walls and generate more pressure. Personally the way I see it is it doesn't matter whether 5 litres or 500 litres, without an expansion vessel, somewhere to accumulate the expansion then the pressure will rise. Am I wrong?
 
Not the best as manufacturers say straight pipe work
 
A few years ago a friend of mine had fitted a 10 Litre Ariston under sink heater which came supplied with a Ariston PRV, but said he was worried because this PRV also had a NRV and was worried/wondered where the ~ 0.2/0.3 litre expansion could go even though it seems (here anyway) to be accepted that it can be allowed to expand back through the cold water supply provided that the nearest cold water draw off is > 2.8M to ensure that no hot water will issue from this tap (1/2" supply) when opened, (this may be the reason for a "loop"?) (and obviously as long as there is no pressure reducing valve in the cold water supply)

I had a good look at this PRV (Ariston 571730) and here is my take on them.
This PRV is fitted directly on the top of the heater with the cold feed then connected.
They are fitted where the expansion volume is taken up by the cold feed pipe and consist of three components combined in one fitting..... the PRV itself which is in the side branch, you can see a little plastic "lifting gear" which can be used to manually open the PRV or maybe can be used as a air release if the cold water supply has failed or whatever. The second component is a “NRV” (hence the worry) which is fitted in the main body of the valve and opens (downwards) to allow cold water to enter the heater when there is a hot water draw off. I think its main purpose is to act as a anti syphon valve in the event of the cold water supply failing/draining down and keeps the heater full of water, the third component is another “NRV” which is inside the "main" NRV and opens in the opposite direction to allow expanded water to escape into the cold mains, main NRV is ~ 8mm dia and the smaller NRV is ~ 6 mm.
When cold water is admitted to the heater then the main NRV (containing the smaller NRV) will open and allow the heater to fill., the main NRV will then close and as the water expands in the heater then the smaller NRV will open at 1 bar and allow the expansion into the cold feed but will still keep the heater full of water under all conditions.

Are these PRVs allowed/available/fitted in the UK? as they are relatively quite common around here but ony on 5 to 10 litre electric heaters.
 

Attachments

  • Ariston 571730 combination valve..jpg
    Ariston 571730 combination valve..jpg
    38.4 KB · Views: 14
  • Water heater.jpg
    Water heater.jpg
    57.7 KB · Views: 14
Last edited:
Thank you. Can I also ask with the prv. Is the pipe allowed to go to a hepvo trap bar a tundish and be teed in to the waste pipe system with other appliances on it. Or does it need its own waste pipe if doing it this way. Like unvented over 15litres.
 
I'm not up to date with current regs but doesn't it need to be terminated through a visible tundish and exit externally minimising risk of blockage etc?
 
Tesla tun and can go to waste then
 
No they shouldn't and even if it did the tundish will just overflow through the sides and expel the water but wastes do block, in fact on a number of our oil condensing pipes we would drill holes in top of external run so if a waste was to block it wouldn't flood the burner, it's a lot of money in rectification if it does
 
No they shouldn't and even if it did the tundish will just overflow through the sides and expel the water but wastes do block, in fact on a number of our oil condensing pipes we would drill holes in top of external run so if a waste was to block it wouldn't flood the burner, it's a lot of money in rectification if it does

just hope the room the boiler in doesn’t flood had that once took two new boiler out :D
[automerge]1578524496[/automerge]
So it can go on to a waste pipe with over appliances on the run?

correct
 
No they shouldn't and even if it did the tundish will just overflow through the sides and expel the water but wastes do block, in fact on a number of our oil condensing pipes we would drill holes in top of external run so if a waste was to block it wouldn't flood the burner, it's a lot of money in rectification if it does

Just using a bit of common sense, there has to be a un restricted drain/vent, (ie into a tundish) from the PRV otherwise a pressure relief valve which I prefer to call a safety valve can become a pressure reducing valve in the event of blockage of the drain which can result in catastrophic rupture, tundish overflowing/flooding or whatever are meaningless really in this context.
 

Reply to 7 litre invented under sink heater in the USA area at PlumbersForums.net

Similar plumbing topics

Does any one know why electric instantaneous under sink heaters are not permitted to me fit to monoblock taps? At least the Hyco ones say not to.
Replies
6
Views
891
Hello, First time posting here, I'm looking for some advice. Apologies in advance if I ask silly questions. I'm English but recently moved to...
Replies
2
Views
1K
I have moved plumbing pipes for Ariston lux water heater As far as I can tell have moved and installed all pipe work correctly Fitted expansion...
Replies
0
Views
2K
Hi to all in the forum! I have a 6 bar pressure relief valve attached to an under sink heater and it was always dribbling a bit. Today, I finally...
Replies
2
Views
1K
Hi, New to this forum and also complete novice who knows pretty much nothing about plumbing. However I have done quite some google searching...
Replies
5
Views
5K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock