Hi to all in the forum!

I have a 6 bar pressure relief valve attached to an under sink heater and it was always dribbling a bit. Today, I finally bought a new pressure gauge and was astounded to measure the pressure at 7 bar!

I usually find most mains to be between 2-3 bar and so it seems ridiculous for it to be so high. The job is in the middle of Bath in Somerset.

What's the highest that anyone has seen?
 
What's the highest that anyone has seen?
More than 10 bar is not uncommon in the UK, I've known ca 15 bar in one place. There is no specified maximum and supply companies do mess around with the pressure sometimes, although they rarely raise it. Increased pressure is worth reporting to the supply company if you want it reduced. There is a minimum spec but it's less than 1 bar (0.7 bar IIRC).

You need a G3 qualified plumber to install a pressure reduction valve to take the pressure down to 3bar and review the safety of your system, which seems a bit dodgy going by your description. Post a couple of pictures if you want more specific comments.
 
If the incoming supply is more than 4 bar then the unvented heater should have the appropriate kit fitted . Kop
 

Attachments

  • Screenshot_20210429-191621~2.png
    Screenshot_20210429-191621~2.png
    378.4 KB · Views: 5

Reply to Crazy high mains pressure in the USA area at PlumbersForums.net

Similar plumbing topics

Hello. I am a homeowner and have a Valliant EcoTech 835 (2017). Serviced every year and worked like a treat until about a few months ago when I notified the pressure reading was too high (> 3 bar). My plumber came and did a regular service and told me the boiler is in tip top condition. The...
Replies
1
Views
298
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air gap as I was having dripping from the pressure relief valve. Since then I've lost a lot of pressure from the hot water feed to my shower. The rest of...
Replies
8
Views
269
I have a bathroom in my first-floor loft conversion. The header tank for the vented boiler is located as high as possible but the sink tap is just above the head of water so obviously the pump cannot self-start. A momentary activation of the bath tap overcomes the problem but it’s not very...
Replies
1
Views
276
Hi, I have a PRV located in a heated plant room that is between a pair of stop cocks. It was installed to keep pressure under 3 Bar a couple of years ago but I have noticed an area of verdigris on the piece from the main body to the gauge. I wondered if this might be sign of a leak / trouble or...
Replies
9
Views
464
Hi everyone just checking if this is right regarding water pressure and combi boiler pressure: Do hot and cold water always vary in pressure such as the following? Cold water from tap filled 1 litre jug in 2 seconds Hot water from tap filled 1 litre jug in 5 seconds Gas combi boiler pressure...
Replies
3
Views
658
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock