My boiler is a Potterton Puma 80. Its old but very well maintained and was working perfectly before my builder modified my central heating system.

I contracted a builder to build a small extension to my home. During the extension work the builder’s plumbing guy fitted two motorised valves. His logic was to enable independent control of the central heating temperatures in the main house independently from the extension.

The work was done in the winter and seemed to work fine apart from a few occasions when the pilot light went out for no obvious reason known to me, however pushing the piezo igniter re-lit the pilot flame and then the boiler would continue as normal. Keeping in mind, because of the cold weather either zoned heating circuit or both would be on and DHW.

Now Easter is here and with it the warm weather there is no demand for heat from either heated zone. So the motorised valves are both turned off. I noticed a boiling sound, (Kettling sound) coming from my boiler. Then the boiler shut down with the pilot light extinguished and the pump now running all the time.

On checking the boiler the pressure in the system was very nearly down to zero. I tried to re-pressure the system via the filler loop, but this was not possible, because of the motorised valves being both off had effectively isolated all the radiators in the house and extension from the boiler.

I found by turning the motorised valves on, effectively demanding hot water. I could now re-pressurise the boiler to 1.25 bar via the filler loop. Everything then worked as normally. However when I turned off both the motorised valves, the boiler kettled and shut down again with a loss of system pressure.

Any suggestions/advice would be very much appreciated.
 
You seem to be saying that the boiler is operating when both zone valves are closed. If so, how is water circulating through the boiler, which is necessary to prevent it overheating?
 
Hi Chuck,
That's what I was worried about. However I think the boiler allows the central heating to be switched off, but in the switch settings shown in the photo's it should still be able to supply hot water.

IMG_2404.JPG


IMG_2402.JPG


IMG_2403.JPG
 
I may be being thick but the valves won’t stop pressurisation as the water will just back fill round the return. If it was working fine then I’d question that the builder/plumber have done anything wrong. Things do break down you know and I’d say your boiler is not the newest
 
Hi Riley,
Keeping in mind I am not a plumber, just a very experienced DIY'er. The boiler was completely rebuilt instead of being replaced about 2 years ago, complete with a full system, rads and pipe flush/power clean. I agree with you in part, but it still doesn't explain why the system cannot be pressurised unless the zone valves are on.
 
Where is the filling loop attached. There’s no logic to what you’re saying unless there is a non return valve on the system somewhere system doesn’t just fill in the flow direction
 
And it doesn’t matter if it’s been rebuilt things still breakdown. If the system was working and now it’s not it is unlikely to be anyone’s fault
 
Sorry to sound blunt but your title is immediately accusatory. If in fact it was a builder or a plumber that worked on the boiler and not a gas safe engineer then I’m afraid the fault lies with you
 
My first thought yesterday was the check valve on the filler loop could be blocked. So I replace the filler loop. On removal I examined the non return valve and it was working fine. The attached photo shows the filler loop. The 15mm pipe is a spur from the mains water feed. The 22mm pipe feeds directly into the boiler's flow and return circuit.

IMG_2405.JPG
 
So I maintain there is literally no reason why it shouldn’t go up as well as down to the two motorised valves
 
Riley I accept I may have hired a competent building contractor who may have used a non certified plumber. I don't know. Yup hands up my fault for not asking to see his credentials, but that is not clarifying the problem. I think the crux of the problem is all radiators are effectively locked out of the system, (Flow and Return) when both motorised valves are either off or not DHW.
 
I agree of course it couldn't fill if the check valve was stuck . That's why I started out by replacing it. That's when I realised the Motorised valves literally take all radiators out of the circuit. Opening the motorised valves allow the system to be re-pressurised.
 
That would be the first thing I’d check, did the builder in fact use a gas safe engineer or just a builder mate of his that does a bit of pipework. You should have an auto bypass in place which will link flow and return to allow heat dissipation once both valves are shut. If the pressure won’t backfill round the return then it sounds like a poor system design. Ultimately without actual sight of the install it’s tricky to diagnose but fundamentally as I’ve said unless there is a non return valve some where on the system then that’s really the only reason that you can’t top up the pressure with the valves closed
 
Originally before the addition of the motorised valves the only thermostats controlling the on off of the boiler, rads and whole central heating system was 1. the boilers own internal thermostat monitoring the water temperature in the system and 2. Each radiator barring two are fitted with TRV's. When the builders plumber modified the system he installed the two motorised valves. He said they are to create two independent heated zones, but they both only work on the radiators. 1. Disconnects the radiators in the extension the other motorised valve 2. Effectively disconnects the main house radiators for heating. Turning both the motorised valves off is now the same as capping off every radiator in the house and the extension. Can a central heating boiler run correctly if it is only heating the hot water supplied to the hot water taps?
 
Yes because the heat will dissipate correctly. You don’t have the heating on in summer do you but you will still have hot water
 
In fairness he should’ve zoned the water as well as you should have temp control over that too
 
If I accept what you are saying and I bow to your superior knowledge. I don't need to call the builder back. I just need a competent Gas Safe plumber to investigate and fix the problem? Know any good and qualified trustworthy central heating engineers in the North West London area?
 
But not if the hot water is unzoned it would go round the coil and back to the primary return then it could back fill
 
They should really have a) piped in a bypass and b) piped the filling loop to the return side as this would alleviate the filling issue slightly. To be fair when properly filling you should manually lock open the zone valves anyway using the levers on them. The filling loop isn’t really a problem as you can do the levers. The bypass is. I’m calling builder or non qualified/educated install
 
I am not 100% sure on what you are suggesting, but I think you are advising that the Potterton Puma 80 boiler (Combination boiler) as installed in my system. Was probably OK before the central heating side, (Pipe and radiator side) was modified. I therefore need to call the builder back to address the issue which appears to be caused by no effective by pass fitted when the pipe work was modified?
 
Don’t call a builder. Builders build plumbers plumb. They have the right idea in so much as the house sounds like it should be zoned but a bypass will deal with heat once the heating requirement is satisfied
 
So I maintain there is literally no reason why it shouldn’t go up as well as down to the two motorised valves

The filling loop is on the flow. On that boiler the diverter valve opens when the diverter valve gets up to a certain temperature causing it to open.

I will remain with what I said before get them back as if its firing when both valves are shut it will be a simple wiring fault. Also ask them to put a bypass on it as I said in my last post.
 
Thanks Riley, the only problem I now have is, the extension build is new and I have not signed off on the builder's snagging list. So a small final payment is due. I don't know whether I should trust him to put it right or to call in a known good plumber to rectify his work. o_O
 
Were it me I would insist on a proper plumber and tell him you’ll be knocking the difference off his bill. He may, fairly, insist on being given the chance to put it right. What has been done is 90% right in terms of building regs but it’s Your call really.
Two questions:
Who rebuilt such an old boiler?
Do you have a thermostat in each zone?
 
No I think it’s as Bogrodder said there’s a non return on the diverter
 
Last edited:
In answer to your two questions:
1. It was rebuilt by a tech specialist from the company that now owns Potterton. I had an expensive maintenance contract with British gas. During one of their service visits their engineer bodged and damaged the boiler. I refused to accept a new Worcester Boch as a replacement. The rebuild was paid for by British gas after a long running dispute where they finally admitted liability.

2. Each zone is controlled by separately wired "Floureon heating thermostats". They are highly accurate I have tested them with an infra red sensing meter.
 
Hi Millsy,

My reasoning was. The existing boiler was the most reliable I have ever owned. It had given me 25 years’ service at the point when it was bodged. It had always been maintained to a good standard. I have always been fan of the old saying “If it aint broke don’t fix or replace it”.

In another home I had a boiler new in 1964, by Valliant. It was still working fine when I sold the home in 2003. Both boilers were always properly maintained.

I had considered the Worcester Boch, but had heard they were only slightly more efficient and could be troublesome unless I was replacing the entire system, pipes and rads. My own research led me to believe I would be lucky to get seven years from one - WB.
 
I’d imagine efficiency wise you are far worse off but I do agree with your adage re if it ain’t broke. Plus I’d imagine parts will be scarce for the puma in the next few years. Did you not also say you’d had new pipework etc?
 
No not new pipe work. I had the whole system cleaned by a guy specialising in power flushing, that's all he did. He forward and reverse power flushed to remove the debris that had collected in the radiators and the pipe work. All rads where individually disconnected and power flushed. This was after the whole system had been flushed through. The process took five hours from start to finish.
 
In retrospect I probably should have gone for a new boiler, maybe a Valliant. I had checked spares availability for the Puma range before making my decision and was told the heat exchanger for the Puma 100 had been discontinued, but all parts were still available for the 80. However that was 2 years ago.
 
It’s amazing how quick things change but if your boiler is in good working order then I keep everything crossed for you that you don’t require any further repairs any time soon. Anyway keep us updated as to how you resolve the bypass issue
 
I am surprised "well maintained" and "British Gas" cropped up in the same sentence,TBH.

And, to be pedantic, the filling loop NRV should be on the Cold mains side.
 
Not doubting you but why??? It always made sense to me when there are two taps but in the instance where it’s tap hose nrv it makes sense because you’d never be able to remove the hose correctly
 
Not doubting you but why??? It always made sense to me when there are two taps but in the instance where it’s tap hose nrv it makes sense because you’d never be able to remove the hose correctly

It was my understanding that you required two taps by regs anyway?

You can see why you have the NRV on the cold, as it's less of a dead leg.
 
But there’s no dead leg because the hose should be removed, alright maybe mm in it but seriously.
 

Reply to Has my builder ruined my boiler? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator...
Replies
2
Views
147
Hello, We had an extension built seven years ago. Initially the builders' plumber connected the heating to the house system but this didn't work...
Replies
23
Views
833
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
450
I have an older gas boiler HW heating system with a taco circulator pump for each zone that worked fine last season. When turning it on for the...
Replies
4
Views
478
Hi, Sorry if question already answered in previous posts, but I can't find a solution to the below: We recently moved house to a new home that...
Replies
7
Views
541
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock