nowucit

Hi Guys,

Went to service the above today, followed MI, fan pressure good -5.87 but decided to give it a full service as its good for my own experience as I'm new to the trade.

All went well cleaned combustion chamber, burner etc, replaced seals as required by MI, then I hit a snag ... The gas valve adjustment screw for CO2 at Hi rate isn't there?? MI (page 53, 5.3) says use a flat blade screwdriver at point B, but there is no screw at point B which I'm assuming is top left? Just looks like its blanked inside. have these valves changed or am I missing something painstakingly obvious, at first I thought it may have a plug covering it but it doesn't seem to .... Any help would be greatly appreciated as I'm completely baffled and feeling like a useful nob :(

http://www.worcesterboilerparts.com...-for-greenstar-cdi--discontinued-april-07.pdf
 
It may have the newer type gas valve, in this case adjustment for high & low made on valve itself.

If the bit you say looked capped off, then it may just be the protection cap! You need to stab a small screwdriver thru it & prize it off! Behind there is the adjusting screw! The protecting cap has a small flat type screwdriver Indent on it but that is not the bit you turn!...
 
It may have the newer type gas valve, in this case adjustment for high & low made on valve itself.

If the bit you say looked capped off, then it may just be the protection cap! You need to stab a small screwdriver thru it & prize it off! Behind there is the adjusting screw! The protecting cap has a small flat type screwdriver Indent on it but that is not the bit you turn!...

page 7 item 24 whip of the protection cover as stated above and adjustment screw underneath.

good rule of thumb in this world, if it aint broke leave it alone!
 
Do not adjust the high fire on the blanked newer type sit gas valve on the CDi ( fine on Ri,Si,junior,I system) or you will screw the readings, the high fire is under a grey cover inside the combustion chamber.

Do not attempt to make ANY adjustments at all on the new CDI compact range, they are fixed via an injector in the gas valve outlet.
 
@lameplumber, thanks very much, would have thought MI would have been a bit clearer but I suppose they are once you know your way around haha :)


@vern, thanks for that I'll make a note :)

All I'm looking to do is to adjust CO2 to MI where necessary. I have read loads on the forum about improperly adjusted CO2 settings and I'm starting to see why
 
Status
Not open for further replies.

Reply to Worcester 30CDI setting gas/air ratio in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi All, I'm looking into changing my conventional boiler (Worcester 30CDi conventional) to a Worcester Greenstar 8000 Style 30kW Combi. My house...
Replies
1
Views
964
    • Like
Hi all, We recently purchased a house and nothing seems to work correctly here, I've spent weeks rectifying issues. Plumbing, electrical...
Replies
47
Views
5K
  • Locked
I have my initial gas safe inspection coming up after successfully completing my ACS a few weeks ago - and, it's fair to say i'm slightly nervous...
Replies
10
Views
4K
N
  • Locked
Serviced the above the other day which I was told hadn't been serviced for around 4 years and before that BG has done it on contract and were in...
Replies
25
Views
252
V
S
  • Locked
Hi all I am a qualified electrical and mechanical engineer but not gas safe so used an 'old school' but very clever plumber for the gas part of...
Replies
0
Views
6K
squarepeg
S
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock