Went to service the above today, followed MI, fan pressure good -5.87 but decided to give it a full service as its good for my own experience as I'm new to the trade.

All went well cleaned combustion chamber, burner etc, replaced seals as required by MI, then I hit a snag ... The gas valve adjustment screw for CO2 at Hi rate isn't there?? MI (page 53, 5.3) says use a flat blade screwdriver at point B, but there is no screw at point B which I'm assuming is top left? Just looks like its blanked inside. have these valves changed or am I missing something painstakingly obvious, at first I thought it may have a plug covering it but it doesn't seem to .... Any help would be greatly appreciated as I'm completely baffled and feeling like a useful nob :(

http://www.worcesterboilerparts.com...-for-greenstar-cdi--discontinued-april-07.pdf
 
It may have the newer type gas valve, in this case adjustment for high & low made on valve itself.

If the bit you say looked capped off, then it may just be the protection cap! You need to stab a small screwdriver thru it & prize it off! Behind there is the adjusting screw! The protecting cap has a small flat type screwdriver Indent on it but that is not the bit you turn!...
 
It may have the newer type gas valve, in this case adjustment for high & low made on valve itself.

If the bit you say looked capped off, then it may just be the protection cap! You need to stab a small screwdriver thru it & prize it off! Behind there is the adjusting screw! The protecting cap has a small flat type screwdriver Indent on it but that is not the bit you turn!...

page 7 item 24 whip of the protection cover as stated above and adjustment screw underneath.

good rule of thumb in this world, if it aint broke leave it alone!
 
Do not adjust the high fire on the blanked newer type sit gas valve on the CDi ( fine on Ri,Si,junior,I system) or you will screw the readings, the high fire is under a grey cover inside the combustion chamber.

Do not attempt to make ANY adjustments at all on the new CDI compact range, they are fixed via an injector in the gas valve outlet.
 
@lameplumber, thanks very much, would have thought MI would have been a bit clearer but I suppose they are once you know your way around haha :)


@vern, thanks for that I'll make a note :)

All I'm looking to do is to adjust CO2 to MI where necessary. I have read loads on the forum about improperly adjusted CO2 settings and I'm starting to see why
 
Status
Not open for further replies.

Reply to Worcester 30CDI setting gas/air ratio in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
523
Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer are) and one of the guys there reckoned it might be "The Gap". I went to the new stockist and the guy there disagreed it was "The Gap" and that he'd...
Replies
2
Views
163
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
302
Hello all, I'm would like to extend an existing outside tap to another point in the garden. I'm about to pour a concrete patio and was hoping to run the water line underneath. There are existing drain (and who knows what) pipes running along the same wall so I'm nervous about digging too far...
Replies
6
Views
264
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
397
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock