Very hard to say without seeing but if the discharge is run in 15mm it ain’t right
 
Even if it is piped perfectly then the TPRV will discharge water every time the cylinder heats as there is no place for the expansion volume to go in the event of a punctured E.vessel bladder or no airend air (as in this case) except that it can expand back through the cold feed?
 
Riley - Noted and thanks. John.g - I suspect you may have hit the nail on the head. I imagine, from what has been said, that if I either turn off the boiler and let the DHW go cold or draw off a significant amount of hot water and then let the boiler reheat the cool/cold cylinder, I should see signs in the tundish of water discharging from theTPRV as the water in the cylinder expands and has nowhere to go as the airless EV is not functioning?
 
When the water is heated and there is no room for expansion (for whatever reason) then the 6bar expansion relief valve will discharge through D1 to tundish and then through D2 and out. Water should not expand back into the system through the double check valve
 
Hi Paul I’m going to have to stop it there mate as you are fishing for info we will not give. Sorry my friend please take the advice given before and get an engineer in with the relevant qualifications.
 
Status
Not open for further replies.

Reply to What is causing water to come from overflow pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello everyone. New to the forum and looking for assistance / advice. I live in a rented house with a not very co-operative landlord. I have just...
Replies
3
Views
212
This issue arose about a year ago. Does anyone have an idea why I occasionally hear (about once every hour or longer) a hammer related noise...
Replies
0
Views
400
  • Question
My disabled daughter’s hot water has stopped working. It’s a relatively modern Potterton boiler with an indirect sealed hot water system and a...
Replies
12
Views
929
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
505
losing pressure
L
I live in an apartment block where generally hot water is supplied from the communal hot water cylinder and cold water to bathrooms is supplied...
Replies
4
Views
636
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock