Have you done your own tests or just going on the information from customer/waterboard?
 
18lpm without. 2.2bar pressure at shower upstairs.

Customer wants more pressure as they have 25lpm at tap downstairs. 4.5bar pressure.


You need to look further into that. There's too big a difference.
If you are measuring 4.5 downstairs in a 'normal house' I would be expecting 4.0 in the loft, or there and there about's. How can it have lost 2.3 bar ?

How did you measure the upstairs pressure?
 
Just read the original post again.

If you are measuring the Shower water pressure, (presume this is off the new cylinder)? You are measuring it after the Governor/Regulator.

If you increase the pipe size from 15 - 22 you will reduce the frictional losses. To calculate the amount you need to know route, distance, how many bends/elbows etc.

To measure the pressure loss through the supply to the cylinder you would need to know the Dynamic Pressure before the water governor on the cylinder and the same at the stop tap at the same flow rate.

I don't know if this helps?
 
Thanks rik. That's what I meant sorry. Just like standing and working pressure at a meter.

Thanks for reply last plumber. So let's say we know the dynamic pressure at the stopcock and before the pressure reducing valve. What calculation would you then use to work out what you would potentially gain by upgrading the pipe?
Its okay knowing pressures prior to the cylinder pressure red valve and at the stopcock but they won't be the same due to the height the water is traveling and the restrictions in the pipe work. I.e bends and sockets.
I would assume that pressure at stopcock and flow rate would be all that was needed to work out what pressure you would achieve the other end of the pipe.

For example 25lpm and 4 bar at stopcock would reduce pressure by 0.2lpm for every mtre of horizontal pipe. 0.4 every meter of vertical. 0.2 for every bend, 0.1 for every socket.

Surely someone must have come up with a simple equation like that?
 
Thanks rik. That's what I meant sorry. Just like standing and working pressure at a meter.

Thanks for reply last plumber. So let's say we know the dynamic pressure at the stopcock and before the pressure reducing valve. What calculation would you then use to work out what you would potentially gain by upgrading the pipe?
Its okay knowing pressures prior to the cylinder pressure red valve and at the stopcock but they won't be the same due to the height the water is traveling and the restrictions in the pipe work. I.e bends and sockets.
I would assume that pressure at stopcock and flow rate would be all that was needed to work out what pressure you would achieve the other end of the pipe.

For example 25lpm and 4 bar at stopcock would reduce pressure by 0.2lpm for every mtre of horizontal pipe. 0.4 every meter of vertical. 0.2 for every bend, 0.1 for every socket.

Surely someone must have come up with a simple equation like that?



If you have 25 lpm and 4 bar at the main stop tap and you pipe the Cylinder in 22 mm tube it will sort it, yes. I think @ShaunCorbs said that earlier on in the thread.

As far as equations go, yes there are equations for water pipe sizing just like there are for just about anything you want to work with.

@steadyon posted a link to some of them.

Have you looked at those?
 
Status
Not open for further replies.

Reply to Way to work out flow rates in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I have quite low flow rate for my electric shower (a piddling 5L/min), and would like some tips or advice about how to solve or find the...
Replies
14
Views
892
Essaboy
E
Hi Could I ask for some help with a water flow rate problem. I have good mains water pressure on the ground floor. There is no tank in the loft...
Replies
24
Views
1K
The Water Board have just replaced the main water supply to our property. We have a ground floor combi boiler. The central heating system for the...
Replies
9
Views
560
Hello, First post, be gentle! Anyway, here's my issue. I have a Roca The Gap D-Trit close-couple toilet with integrated macerator in my secondary...
Replies
9
Views
729
Looking for any ideas to help. I've a Heatrae Sadia Hot Water tank, heated through Oil fired boiler (working fine). A week ago I reset the air...
Replies
8
Views
345
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock