Hi Riley,

I have two types of valves on my system; the first type are bi-directional (these: http://www.NoLinkingToThis/p/white-chrome-angled-trv-15mm/60368)

and the second type are tradiaitonal valves that can be used at either end (these: Traditional Chrome Angled Radiator Valves Pair 15mm)
 
Hi guys,

A quick update.

I flushed the rads manually with a hose pipe a couple of weeks ago and when I drained a rad last night to add Sentinel X300 the water was clear.

However when I removed the bleed valve to dose the chemical loads of carp started coming out of the rad. This is a tiny rad! Now the pump in the boiler only seems to work on 'max' when there is a demand for hot water and doesn't seem to work as hard as when there is a demand for heating.

Is this normal in a system that is only a couple of months old? The original plumber did say that there was an unusually large amount of debris in the radiators given they were brand new.

image.jpg
 
No that's not normal but can happen needs to be flushed, chemicals in leave it as long as possible read the instructions and if you can take each rad off and flush with hose while beating gentle with a rubber mallet

aldo do you have a mag filter by the boiler ??
 
I would be getting onto the radiator company as well as I bet they weren't cheap Y
 
Thanks guys. I really appreciate your help as the house renovation has been so stressful and this is topping it off! Especially considering

Yes I have a magna clean but none of these particles are being trapped. The water samples are all clear - it's just when I took the bleed valve off that I noticed all of these debris particles coming out!

Do you think it's worth asking the radiator company to pay for the power flush?
 
Thanks guys. I really appreciate your help as the house renovation has been so stressful and this is topping it off! Especially considering

Yes I have a magna clean but none of these particles are being trapped. The water samples are all clear - it's just when I took the bleed valve off that I noticed all of these debris particles coming out!

Do you think it's worth asking the radiator company to pay for the power flush?

You could ask but bet you there's something in the small print saying must flush the rads out first :D
 
Just checked the instructions and it says I must flush the heating system out first not the radiators (the plumber did this when commissioning the boiler). I will write to them and see what they say.

What I'm concerned about is each of these radiators having some debris in them and when the boiler was fired up it circulated the debris and it's all collected somewhere which is causing the poor circulation. Don't know what il do if I have to rip floors and carpets up!

So weird that the water is clear when draining and in the magna clean but there is a load of carp near the bleed valve that seeped out when I added the chemicals!
 
Sometimes carp does collect at the threads. I think there's more to th than meets the eye. Do any of the radiators warm up properly
 
Yes some of them warm up more than others. If I turn off all valves apart from one rad then that one gets roasting.

Just read up on 'sludge Flakes' and I'm worried that my picture shows them. Apparently they're difficult to remove with a power flush. Getting really worries now as the system was piped in uponor so unlikely that there was any flux etc left in there and that all these flakes have come from the radiators and have collected somewhere and we won't be able to remove them.
 
The positive being that if each rad will get hot when it's on on its own then you have circulation.
 
Thanks Riley.

One radiator in particular only gets lukewarm when I isolate it. 90% of the others get hot. Is that a bad sign?

Unfortunately that's the one with pipes under our tiled floor!
 
There's nothing to say that the pipes for that rad can't be isolated at either end
 
Hi guys,

Me again!

Just thought I'd keep this post updated in case anyone reads this thread and has similar problems.

Had the installer in today and we've ruled out blockages in the pipe work and the radiators being piped wrongly.

If you remember - the boiler heats the hot water really well (burner on max and flow temp at 70 degrees) but when the demand for hot water was satisfied it started hearing the rads but flow temperature would start at 70 degrees and then lower until it hovered around 45 degrees. This happened even though we disconnected the Internet (so no weather compensator data used), the room stat in the fridge (3 degrees) and 'comfort override' mode on.

We then tricked the boiler when it was heating hot water to heat the rads instead (at 70 degrees with burner on max) by manually opening the motorised zone valve. All of the radiators (bar a couple that had dodgy valves which we've now fixed) and all the rads were roasting. So the pipe work and rads are fine.

So the installer thinks it might be the controls. However Vaillant have come out twice and not identified the problem. I think it might be the fact that the boiler is oversized (30kw but have 14 rads over 4 floors plus unvented cylinder) so it might be in anti-cycling mode? What do you think?
 
I still think it's something to do with weather comp it's the only thing other than somthing drastic as its prity much all standard kit wired to s plan
 
Thanks Shaun.

Why do you think that is please?

As far as I'm aware the weather comp data is collected from the Internet so with that switched off it has to rely on the room stat which was sat in the fridge?

Tempted to get a bloody basic on / off switch instead!!
 
I do agree with Shaun re the symptoms. I just can't see how with a v smart as there's no external sensors
 
The reason I say is if it was one of the controls not much on the heating side port valve and room stat it would be doing it for both heating and hot water

The only way other than to remove anything regarding weather comp is wait for the cold weather and see if it heats up then

Unless you could trick the weather comp to think you living in the North Pole if you have to set it manually where you live ??
 
Hang on hang on hang on just re-read your first post do you have a room thermostat in addition to the one that comes with the V-smart
 
Sorry Riley!

I have the vsmart which comprises of a VR65 wiring centre and a separate room stat (comes in the same box)
 
I'm reckoning wiring fault did Vaillant guy check wiring
 
We then tricked the boiler when it was heating hot water to heat the rads instead (at 70 degrees with burner on max) by manually opening the motorised zone valve. All of the radiators (bar a couple that had dodgy valves which we've now fixed) and all the rads were roasting. So the pipe work and rads are fine.

By doing what I said in post 45, 3 weeks ago you would have proved this.
 
I'd get Vaillant back mate you've proven the system works
 
Thanks Riley - I will get them back. They said to change the range rating on the boiler downwards but that's had no effect. I understand from searching other forums that I'm not the first to have had this problem.

Stoned Ground - fantastic advice thank you. I showed your post to my installer (he probably hates me now!) and he followed those instructions to identify the issue.

I will keep you posted on what happens next.
 
Sometimes it's easier to take away external controls to prove they are or aren't the problem. Maybe ask Vaillant to send a senior technician they need to prove to you there is not a fault with their system.

Have they tried a full factory reset of boiler and controls?
 
I thought it might help if I took the boiler from 'auto' under the heating load to the actual load.

I have calculated my rad heat output as 18,137kw so how much should I allow for my unvented cylinder please? 2kw? Would it then be a good idea to set the heating load at 22kw?

Thanks again guys!
 
Right you've proven that your radiators get hot yes ?
You did this by essentially taking the zone valve out of the equation?
I think you are looking at a control or a wiring issue
I'm not sure that there is a kilowatt loadage issue
 
Hi Riley,

Thanks again for your support. Your advice has been incredibly helpful and generous.

Yes we have established that the rads get hot (by manually opening the zone valve when the boiler 'thought' it was heating hot water) so the installer agrees and thinks it's a wiring/control issue.

I thought adjusting the load might help as I wonder if the boiler is going into anti-cycling mode too quickly if its oversized? It's probably something as simple as the wiring or controls but I've read other forums that have posts with similar problems to mine and that's what they suggested.
 
Have you got Vaillant coming back I think you are just clutching at straws a bit at the moment mate you need to go at this with a plan rather than just randomly changing stuff in the hope that it will fix it. My suspicion would be that there is an issue with the wiring centre
 
Last edited:
Yes mate - they're coming out on Monday.

Ok will gladly follow your advice and leave well alone this weekend. Will keep this thread updated once they've visited.
 
Thank you for keeping us updated and I wouldn't think changing the kw setting of it would matter too much
 
I've just skim read all this so excuse me if I cover something that has been dealt with or if i've missed the point entirely and please do not take offence at anything. Like I say it's a massive thread and I may have missed vital parts of the conversation.

If that Heating MV when opened manually, allows the heating to work, Why has It not been changed or at least inspected ? How do you know the paddle or ball isn't broken or clogged ?

I have seen the rubber ball type swell once due to heat and also once due to an overdose of inhibitor. That would give the symptoms you describe.

Also I did not see what the rads are made of but if they are cast iron, could it be casting sand left inside that has got washed out and into the MV ?

I'd remove that MV and look !

I know it opens manually which would indicate it is not blocked but they don' t always open quite as far by motor .

Again, really sorry if i've missed the point here !
 
Last edited:
What's the Flow and return temp on boiler ?
Both the pipe temps beneath and menu 40 and 41?
 
Has anyone checked that the valve is not slipping on the teeth when opened by the motor.

When you open them manually you shuv the thing open regardless of teeth
 
Status
Not open for further replies.

Reply to Vaillant boiler not heating radiators. Please help! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
132
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
125
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
443
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock