D

DCB

We currently have a Honeywell T4360B room stat; because it's on a 24v control circuit (Glow Worm 30cxi) the anticipator can't be used which, together with the fact that it's a simple mechanical stat, means that we're getting considerable over-run & poor temperature control. Looking at Honeywell's spec sheets I'm 99% sure that a DT90 can be used as a direct replacement - any reason why not?
 
Hi DCB and welcome why not give Honeywell technical a call to confirm or recieve other options regards Turnpin:43:
 
Thanks for the replies!

Honeywell's website says that they are unable to offer technical support to householders; however, I've had another look & found that that only applies to phone support, so I've emailed them.

In answer to your question, Simon, the TP90 uses time-proportional & integral control, so it will control much more precisely than a simple on-off thermostat.
 
Got an almost immediate reply from Honeywell.

So, as we say around here, job's a good'un!
 
Status
Not open for further replies.

Reply to Simple room stat question in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
349
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
578
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
310
PSxxxxxx
P
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
261
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
360
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock