S

sasik

Hi

Is any of you had any problems with Siemens motorised valves?
My client have an "S" plan system and one of the motorised valves (heating) is shut all the time. When I try to put it in the "open" position manually it won't stay! and the boiler won't come on.The other valve (cylinder) seems to work fine (open/shut automatically).For some reason the boiler won't come on at all when the valve for the heating is shut but the valve for the cylinder is open,why? The only way I could get the dam thing to work (temporarily) was to tie the faulty valve in the open position just to keep the boiler running at the weekend.

Your
thought
please
 
Faulty valve! when I try to put in the open position manually it won't stay open. Can it be repaired or I need new valve?

Thanks sasi
 
(heating) is shut all the time.
is it getting power from stat ?
if yes is the motor faulty in the valve ?

When I try to put it in the "open" position manually it won't stay! and the boiler won't come on.
but you say later on the only way to get boiler on is tie it in open position.
it either fires up or it don't.

The other valve (cylinder) seems to work fine (open/shut automatically).

For some reason the boiler won't come on at all when the valve for the heating is shut but the valve for the cylinder is open,why?

if the cylinder stat is calling and the valve is opening is their power on the orange ?

no power on the orange then the microswitch is faulty or you haven't got perm live on the grey.


heating and cylinder zone valves need to be checked on seperate circuits as they don't have nothing to do with each other like a mid position wiring.
 
Hi sonray

Thanks for you reply. what I meant (second quote) is, the small lever on the valve won't stay in the open position as it should so I had to tie it. Only then the boiler will fire.

thanks sasi
 
Hi sonray

for some reason it won't clip into the "open" position. Any reason for that?

Thanks
 
maybe someones forced it before and its broke etc.

as for the boiler kicking in.
the lever on the side is a means of opening the valve when draining or refilling system.
the boiler will fire up when the motor opens the valve because it opens the valve a few mm more than when you open it manual.

if you remove cover it will not activate the microswitch by hand but does by the motor.
 
Hi sasik,

Yes have experienced this problem before on siemens 2 ports. You can lock open to manual which should send permanent live to the boiler but the contact doesn't make!!! if you hold it over into manual it works but clipped into position seems to have too greater separation in the contacts to form the connection. This is a fault that we have experienced and does result in changing the valve. As a temp measure linking the brown to orange (stat call to switched live) and removing head and switching to open would enable a customer to maintain some control,although this would need explaining to the customer
regards rogerp

Regards Rogerp
 
Think it'll be sorted from 2009 mate
 
Status
Not open for further replies.

Reply to Siemens two port valve problems! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
161
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
213
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
327
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
503
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock