So I have a combi, my thermostat is Honeywell dt90e. Wanted to change thermostat to a programmable so bought a 2 wire programmable stat when wired In. The stat is calling for heat but boiler won't fire. I took stat off and connected a wago to both wires and the boiler fires straight away. Has anyone had this before or anyone know what's wrong. Thanks
 
Danfoss has a battery, mains and rf version of this. Can’t seem to find flowmasta version. Are you able to provide photos of wiring?
 
Last edited by a moderator:
because all it is , is a switch so live and switched live ***************

Best you get somebody with knowledge involved .
This
because all it is , is a switch so live and switched live ***************

Best you get somebody with knowledge involved .
Okay glad we cleared that up I have basic knowledge in it, still can't figure why boiler won't fire, because It works when I connect with a wago but not when wired to stay and there's only 2 ports on the stat
 
This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.
 
This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.

This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.
Thank you Timmy D will try that in next few days
edited that for you
No need for that , I understand need a course on it don't do much electrics
 

Reply to Problem with thermostat in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
275
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
180
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
261
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
395
Hi all, I'm installing a concrete patio out back. By the wall under the kitchen sink I have an existing P-Trap gully for the grey water from the sink, dishwasher, washing machine etc. When I pour the concrete there won't be any chance to dig it up anymore. From my own research I get the...
Replies
0
Views
148
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock