So I have a combi, my thermostat is Honeywell dt90e. Wanted to change thermostat to a programmable so bought a 2 wire programmable stat when wired In. The stat is calling for heat but boiler won't fire. I took stat off and connected a wago to both wires and the boiler fires straight away. Has anyone had this before or anyone know what's wrong. Thanks
 
Danfoss has a battery, mains and rf version of this. Can’t seem to find flowmasta version. Are you able to provide photos of wiring?
 
Last edited by a moderator:
because all it is , is a switch so live and switched live ***************

Best you get somebody with knowledge involved .
This
because all it is , is a switch so live and switched live ***************

Best you get somebody with knowledge involved .
Okay glad we cleared that up I have basic knowledge in it, still can't figure why boiler won't fire, because It works when I connect with a wago but not when wired to stay and there's only 2 ports on the stat
 
This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.
 
This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.

This is likely the situation. However, I can’t find the instructions online for the flomasta (Rubbish anyway, bin it).
When you look at the danfoss instructions, that particular model comes with sub models (hard wired, rf wireless, battery hard wired).

You have 2 wires for the old stat. They will be a live connection (common) and a switched live.
You’ve identified the common as per you post where you say it’s connected to the boiler live (this is for safety, so when the boiler is isolated for maintenance, power to the stat is off).

The other wire must be a switched live as there is no other way to signal the boiler to come on. You’ve also proven this by wago linking the two wires.

Now, with this in mind, the replacement stat/programmable stat you choose, need power. You can’t use a hard wired 240v stat, as you’ve not got enough wires to provide a live/neutral/switched live.

So this means we have to use a battery powered unit. It uses battery power to operate itself and switch the incoming common to switched live.

If the common is 240v, it will switch and send back 240v, if the common is 24v, it sends that back.

With the danfoss, the instructions say that the common should be connected to port 2 and the switched live to port 3.

If you’ve got a multimeter, you can check the switch is working using continuity across the ports when the stat is calling/not calling.

If you prove the stat switch is working as above and you’ve proven the wiring with the wago, I’m at a loss.
Thank you Timmy D will try that in next few days
edited that for you
No need for that , I understand need a course on it don't do much electrics
 

Reply to Problem with thermostat in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

A
I have a greenstar 35cdi combi boiler that when the thermostat calls for heat. It will fire up heat to temp and then drop down to 41* on the...
Replies
1
Views
248
Nicholas
N
  • Question
Have a sytem boiler with unvented cylinder with 2 heating zones plus hot water in a house we moved into recently. To start with we were always...
Replies
8
Views
464
H
Wishing everyone on tgmhis forum a very happy Christmas!! I am working on a combi boiler which has problem with heating only. Water is heating...
Replies
2
Views
357
I have bought an old house in rural France and it has an oil tank and Unical oil powered boiler (Italian I think). Its a beast of a thing but...
Replies
6
Views
640
I have a home with an oil boiler in a garage turned into a flat, heating both flat and main house, running c plan with two pumps, two motorised...
Replies
0
Views
422
Back
Top