scoutkim3870

We have an old Potterton Prima B boiler, up until now working fine. We went away for several days, leaving HW and CH on (with rads low). We returned to find everything off and the pilot light out. I re-lit the pilot light and since then it runs for a while (sometimes as long as a whole day), with the HW and CH both working (although the HW does not seem as hot as usual) but then goes out again. Usually (but not always), this is accompanied by a loud noise (from the loft ?) not classic water-hammer, more like a roaring/vibrating kind of noise for a few minutes. I always like to have some understanding of the problem myself before calling for further help, and I’m thinking that perhaps the water in the cylinder is overheating and “boiling” up into the feed and expansion tank, causing the noise. Although of course this does not necessarily tie in with the water not being hot enough. I am thinking that perhaps the problem could be with the diverter valve next to the cylinder malfunctioning. Could I be right about this? Any other ideas? Thank you, in advance, for any help or light on the subject.
 
Last edited by a moderator:
Do you have to re-set the overheat or is there the noise without it tripping out?
 
Yes it always trips out after/at the same time as the noise and I have to reset the overheat.
 
Well it could be a couple of things .... The control thermostats on these are always f'ailing' to hotter than normal is one ... Just put the thermostat to its minimum and see if that stops the overheating. However there's a thing called the pump overrun fitted on these boilers that can sometimes turn the pump off when they switch over. This will give you the symptoms you're describing and would be my hunch if the boiler control stat seemed okay!

There are other possibles but these are the two most likely suspects IMO :)

Get yourself a GasSafe guy in to have a look at it.
 
could be as simple as no water in the header tank but my bet would be sticking pump especially as it started after being turned of for a while
 
Last edited:
Got a qualified gas man in. It was the divertor switch upstairs - motor had burned out, somehow this was causing the boiler to trip out. Anyway, it's replaced now and everything is fine.
 
Status
Not open for further replies.

Reply to Pilot light going out, with loud noises from aloft! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
343
Hi guys....we have an old Astracast sink top....I think its a composite sink....has a big single bowl. My wife thinks it looks scruffy....looks...
Replies
2
Views
237
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
227
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock