Replacing a clients old standard boiler with new oil heatslave 11 combi 18-25. It has a nest wired in and looking on the instructions it says 3amp max to nest but the boiler requests 5amp. Anyone with suggestion around this. Im sure there are plenty nests wired in to oil boilers.
Thanks
[automerge]1573387184[/automerge]
Replacing a clients old standard boiler with new oil heatslave 11 combi 18-25. It has a nest wired in and looking on the instructions it says 3amp max to nest but the boiler requests 5amp. Anyone with suggestion around this. Im sure there are plenty nests wired in to oil boilers.
Thanks
would the oil boiler work of a 3 amp fuse..
 
Last edited:
So you're a qualified sparky Richard? I knew there was more to you lol. Like above downrate fuse and bring boiler on, if 3 amp fuse melts you know the boiler draws more current and the nest isn't suitable. The fuse will protect the nest.
 

Reply to Nest wiring for a new Worcester heatslave 11 combi 18-25 3amp nest 5amp boiler in the USA area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
263
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
291
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
228
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
316
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
501
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock