lolipop

Gas Engineer
Messages
129
Hi guys I ve been to one of these boilers today it's on a y plan the boiler fires but pump does not run ,changed 3 way valve but just the same ,the pump is wired from boiler but getting no live !! I was thinking boiler pcb ????has anyone got experience on this boiler ?? Anyway got hte and hw on by wiring pump straight onto 3 point plug any ideas guys
 
Here is a wiring diagram, looks like the pump is wired in with the pump overrun stat I'd start there
 

Attachments

  • image.jpg
    image.jpg
    95.3 KB · Views: 70
Cheers zbd this drawing very helpful that pump overrun stat needs checking where abouts on boiler is it as this appliance is in the most awkward location
 
This one is not getting repaired it's fitted in an alcove 6 " off the floor ,and 6" gap between front of boiler and cylinder then a built in sliding door and frame to hide it I ve got it running for Christmas for them then a new boiler required
 
I think the pcb goes for around ÂŁ180/ÂŁ190 but other then that and a fan I've been told your be lucky to get anything!
 
The stats on these go too, thats worth checking.

I've no idea if you can still get the stats, been a few years since i changed one.
 
The stat is still available. Part no: 402S088. roughly ÂŁ18.00 inc vat.
Situated at the bottom right hand side at the rear of the combustion chamber on a bracket.
By the sound of it, it would be a t**t to do. You could transfer the pump supply to the boiler SL and lower the boiler temperature as a temporary measure.
 
One of the lightest boilers on the market at the time, loved them!! It will be the overrun, nowt else would cut the pump out except a knackered pump or it's supply wire...! :)
 
Status
Not open for further replies.

Reply to Myson Apollo in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello. I've just replaced our old Potterton EP2 CH controller with a Drayton Wiser HubR (& peripherals). The old backing plate wasn't...
Replies
1
Views
308
Experiencing an issue with a Worcester Greenstar 21i conventional boiler if anyone could help! I have previously installed a Tado smart controls...
Replies
4
Views
722
have moved a pump by new boiler so could wire for pump overrun as no live in airing cupboard, but now I am worried about air ingress into the...
Replies
3
Views
762
    • Like
Hi everyone, Just wanted to share my experience with "upgrading" an S plan setup to Opentherm and Vaillant Control Center (VR66). There are a few...
Replies
1
Views
1K
Customer complains of Intermittent heating on Y plan with Stat satisfied. New boiler fitted last year (no permanent live required or fitted...
Replies
25
Views
2K
Back
Top