TerryWaite

Plumbers Arms member
Plumber
Gas Engineer
Messages
324
Hi

went out to do a cylinder swap to exchange an indirect cylinder that was leaking from the body, more or less a straight swap, slight pipework mods.

On questioning customer, I found the guy had no boiler or heat source for the indirect coil, he had storage heaters for his heating, and the two pipes coming off his indirect coil out of the cylinder went straight up and both terminated like open vents above the f and e tank.

I was going to just cut these out and cap the indirect connections off on the new cylinder (more scrap for me, or the mrs, as she now deals with the scrap) but was slightly reluctant as I thought this must have been done for a reason, so to cover myself I just reconnected them the same way.

Would the heated hot water in the vessel cause the air to pressurise in the coil, to a dangerous presure? Is this a common thing?

Can you get cylinders with just an immersion heater in and no coil?

And also, the cylinder was 900 high, I bought a 23 or 27 " immersion heater but it would not screw in as it was catching on the coil inside. Anyone ever had this problem? I had to go out and get the next size down I think this was a 14" or something, same kilowattage like (3kw) but I am worried that this will only heat the top portion of the cylinder up and maybe the cust. will get a little bit of steaming hot water rather than lots water at the required temp. There was no cylinder stat fitted to old one so I havent fitted on on new one. Immersion heater dial was set to middle and sealed with a spot of gunk. it came like this I assume so as not to be tampered with.

Did I do the right thing?

regards

John
 
Yes you want a Direct cylinder, 27" will fit in with a bit of fiddleing about, 14 " will not give full tank of water, used to fit indirect cylinder as it was cheeper than direct (Strange but true)
 
yes you can get a direct cylinder without a coil

beat me lol
 
if the imersion fouls the coil i usually give the coil a little shove over with a bit of 2x2 timber through the imersion boss the fourteen inch one will only heat the top third of the cylinder not enough to fill a bath you can just leave the coil connectors with the plastic caps on to stop mice spiders and cockroaches getting a warm home
 
The existing cylinder may have been a primatic and that was someones idea of blanking it off rather than capping it (not that capping it would have made any difference on a primatic). Take a grinder to it and have a look.

If the immersion is catching the coil screw a 2 1/4" plug in a few turns and bend the tapping a bit straighter then fit the immersion. A 14" is too small for a 36" cylinder.
 
Ah, the old Primatics, if the bubble went, they were a nightmare.
 
thanks alot, i may have to go round and replace the immersion then, i shall see whether custard complains or not, he said he doesnt use the bath he has an electric shower. But ill be ready for the callanyhow.

Why on earth do they not angle the tapping on the top so that it goes down the middle? seems ludicrous to me! And where would you get a 2 1/4" plug? I thought BSPT pipe thread sizes were 2" and then 2 1/2"??

If you left the indirect coil with the plastic caps on, if the annulus burst inside, would you not flood the house?

regards

John
 
thanks alot, i may have to go round and replace the immersion then, i shall see whether custard complains or not, he said he doesnt use the bath he has an electric shower. But ill be ready for the callanyhow.

Why on earth do they not angle the tapping on the top so that it goes down the middle? seems ludicrous to me! And where would you get a 2 1/4" plug? I thought BSPT pipe thread sizes were 2" and then 2 1/2"??

If you left the indirect coil with the plastic caps on, if the annulus burst inside, would you not flood the house?

regards

John
terry had you never came across a direct cylinder before,i struggle with understanding electrics,but then again i am a plumber,the basics are there..?
 
thanks alot, i may have to go round and replace the immersion then, i shall see whether custard complains or not, he said he doesnt use the bath he has an electric shower. But ill be ready for the callanyhow.

Why on earth do they not angle the tapping on the top so that it goes down the middle? seems ludicrous to me! And where would you get a 2 1/4" plug? I thought BSPT pipe thread sizes were 2" and then 2 1/2"??

If you left the indirect coil with the plastic caps on, if the annulus burst inside, would you not flood the house?

regards

John

Have you been plumbing long mate?
 
Status
Not open for further replies.

Reply to Indirect cylinder used solely as an immersion heater in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two...
Replies
2
Views
227
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
291
Just started gound work on self build bungalow and wondering best way to do below ground soil pipes. For toilet I was going to go straight down...
Replies
2
Views
174
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
343
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock