Glow Worm 30 CXI central heating comes on with no demand from thermostat and even remains on when cenral heating is switched off - I have had to turn power off to stop it - No fault code displayed - also the radiators get warm when hot water is used when i have managed to temporarily switch the boiler back on without constant heating (then in middle of night came on again by itself) ?
 
Hi, sounds like the motorised valve is staying open, letting water pass into heating, therefore rads get hot when taps tuned on, & when boiler calls for hot water preheat. You probaly notice you hot water isn't as hot.
 
Thanks for your diagnosis- much appreciated-yes water only gets really hot when tap only half on - can the motorised valved be excersised and work again or is it best to just replace it?and is it an easy replacement or am i best calling a plumber
 
It's best to get a Gas Safe Engineer who specialises in service & repairs.
 
Hi trokey, did you manage to fix your glowworm , ive just had the same thing happen to our boiler, I installed it 5 yrs ago and its been great up to now, but same symptoms as yours.
Was it the motorized valve?
Thanks, james
 
People ask questions you try to help them but they rarely get back on and let you know the end result its ignorant
 
Status
Not open for further replies.

Reply to Glow Worm 30 CXI radiators get hot with no demand and CH swithed off in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new well maintained Worcester combi boiler. We weren’t convinced the heating was working right and then got hit with a £610 energy bill for the first 6...
Replies
0
Views
275
MartinPod81
M
Fitted a glow worm energy yesterday and is firing for hot water when there isnt a hot water demand, there are no leaks anywhere. Even when heating is calling the hot water demand is still overiding even though no hot taps are open. Has anyone got any ideas?
Replies
6
Views
2K
G
I've just bought a 3-floor house with a gas boiler on the ground floor and hot water tank on the middle floor. When I switch on the hot water at the timer panel, it works but it also heats up all the radiators above ground floor. I have to close them individually to stop this. The rads aren't...
Replies
1
Views
522
M
Hi, Hopefully someone can throw some light on if this is a real issue or not. I have had this boiler for about 10 years, I noticed just recently that when the CH has been turned off that a couple of the rads closest to the boiler were slightly warm. When the boiler had demand to heat the DHW I...
Replies
1
Views
402
Hi All, In Dec 2023 I had my annual boiler service and asked the plumber to change 2 radiator valves as the radiator in the toilet downstairs was not working. He changed both valves and still the radiator was not working. He put some chemicals in and said it should break up anything that is...
Replies
7
Views
499
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock