Can anyone tell me the dew points in kerosene and natural gas condensing boilers please.cant find answer online
 
How accurately do you need the answer? From memory, for natural gas with 10% excess air (for maximum efficiency) the dew point is about 58°C, for oil it's about 49°C.

Don't forget that if you need a boiler to condense a useful fraction of the water vapour in the flue gas you need the return temperature to be significantly (say 5°C or more) lower than the theoretical dew-point.
 
1639523541108.png
 
The big easily got gain with a HE boiler vs a SE boiler is the extra sensible heat extracted from the flue gases due to another Hx installed (called a economiser on steam boilers) which reduces the flue gases by ~ 150C leading to a 7% to 10% gain in efficiency, any condensing effect is a added bonus, fairly easily attained with outside temperature compensation.
 

Reply to Dew point on condensing boilers in the USA area at PlumbersForums.net

Similar plumbing topics

Recently had a Viessmann Vitodens combi boiler installed, quite often when the adjacent cold mixer tap is opened the boiler starts for a few seconds! Can anyone tell me what is causing this? And how to cure?
Replies
3
Views
204
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
264
Hi all, this is probably a daft question but I need to run my cold feed from one side of my wall mounted boiler to the other. Running it beneath the boiler is difficult with lots of obstacles, is it okay if I run soldered copper over / across the top of the boiler? It'll be about 4" off the top...
Replies
1
Views
44
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was prosecuted after Hereford Trading Standards Team found that he was falsely claiming to be on the Gas Safe Register when he was not, putting members of the...
Replies
0
Views
152
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
147
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock