Hi chaps,

Bit of a bugger today - warm flow Utility 150HE , situated in a garage with a balanced low level flue It has gone sooty so cleaned it up changed nozz etc etc but when doing the flue gas analysis , no matter how much I opened up the air intake I could not get enough air. `the only way I could get satisfactory flue gas readings was to detach the snorkel and let the burner run using air from the garage. Anyone else had similar probs before?


many thanks

dave
 
strictly speaking it isnt a balanced flue either, just a room sealed one if it sucks air in one part and blows the fumes out the other part..
 
Also check that when you turned the Allen bolt air adjustment to make sure the wee air door is sliding open. I see a few of them that the threads have stripped on the bolt inside. Take the spigot off and look inside with a torch. Them RDB air adjustment parts are poor.
Also be sure the flue is correct size for that output - ask Warmflow if not sure. I know a Warmflow 150 utility condensing boiler with balanced low level flue that is tending to soot up and Warmflow had previously said wrong flue for this large a boiler and disconnected snorkel apparently.
 
Last edited:
+1 with best , same with a warm flow utility. , plastic damper wasn't moving when turning Allen key . Stripped down put back together all good then .
 
sorry guys -should have said...the plastic damper was working fine / not jammed ,..so opened up fully
 
thanks for all the input fellas - am I OK to let it run now with the snorkel detached

I would be apprehensive about it if the flue seals are knackered you possibly have pocs being discharged into an enclosed area

maybe run a room test with your flugas analyser to check for any co readings
 
see post 2, if that is the probable issue dont even use the boiler until you have replaced the seals! god almighty mess will await you in a few weeks, plus, if the intake seals are gone you may well kill your customers
 
Status
Not open for further replies.

Reply to detach the snorkel on a balanced flue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, came across this forum this looking for information on my sooting up kitchen type indoor Enviromax. I'm a retired electronics/maintenance...
Replies
5
Views
2K
The boiler has just been serviced and lots of new parts fitted, On firing up all works fine for approx 15 seconds then the flame cuts out but the...
Replies
14
Views
3K
Hi Guys, Been having a real saga and head scratching situation. I originally had 1 problem, and now 2. Original issue: Air being built up in...
Replies
17
Views
4K
Hello, from South Devon. Firstly - I'm not a Gas Safe RGI. I'm considering my options to replace a 23 year old |Ideal Classic FanFare 50,000 kw...
Replies
18
Views
3K
Hi Everyone I have a very old Powermax 155 boiler which is 20 years old. A couple of years ago, I had a problem with the burner switch...
Replies
5
Views
2K

Newest Plumbing Threads

Back
Top