I was thinking about the min flow calculation and think we can estimate this using the specific heat capacity of water.

A 35kW combi with a 6,8kW min burn for a 20 degrees jump (say 70/50) gives 6800/(20*1,163) = 292 L/h. The pressure/ motor speed graphs in the manual stop around 200 L/h, suggesting this number is ball-park.
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to Delta 30 or 60 degrees for radiators? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

WB 4000 installed a few months back, just balanced the 7 rads - managed to get around 15 degrees delta across most rads. Not quite the 20 degrees...
Replies
2
Views
635
Hi all Having some renovations done on ground floor and looking to get rid of / replace some of the older looking boilers on that floor (mainly...
Replies
16
Views
2K
  • Question
Hi all. I recently upgraded our CH system, but rather than the expected drop in gas consumption, Octopus is saying we're using roughly 30% more...
Replies
19
Views
919
Hi, moved into a home a year ago with what is probably an old heating system. There is a gas boiler linking to radiator central heating, and a...
Replies
4
Views
583
Hi, I have an 20yrs heat only potterton 50e boiler with 196x old house - suspended floor - designer radiators, open vent system and hot water...
Replies
1
Views
622
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock