I'm setting up a small brewery and need the ability to have instant hot water at decent flow rates.
I've been looking at commercial options but I was wondering if anyone can recommend a good unit that can get unto 80?

Appreciate any guidance!
 
If you mean up to 80 degrees C, the laws of physics are against you.
A 'decent flow rate' would be say 15 litres per minute?
Say your incoming cold water supply is at 10 degrees C, and you wanted hot water at 80 degrees C, that means heating water flowing at 15lpm by 70 Degrees. That takes about 65 kW according to my reckoning.
That needs a big 3 phase electricity supply, or a big gas pipe!
If you could manage with a more modest flow of say 10lpm, heated instantaneously, that would still need 44kW.

You would stand a better chance of getting both high temperature and high flow rate with a stored hot water option.

As per Undertrained, giving more info about what you want to do would help.

EDIT: Were you thinking of going electric or gas for this?
Maybe you already have a 3-phase electricity supply, or a larger capacity gas meter/supply?
 
Last edited:

Reply to Continuous Flow Hot Water System - Highest Temperature in the USA area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
126
Hi, My current hot water system needs to be replaced. Anyone got any suggestions or can recommend any plumbers around Derrimut area that won't rip me off? An office guy recommended me to apply for government rebates and get it installed through timetosave.com.au. How reliable is this...
Replies
6
Views
293
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
277
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
115
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock