Yep plenty more room up there. All right having 4 tanks but trying to fill them up off a 15mm main is not ideal hey
I'm not surprised they are running out with that set up.
If they have all 10 showers on simultaneously, running at say 10L/min then that's 100L/min of flow. Average shower length is 5-6 mins. So 600L of 40 degree water required for 10 showers. So 1 x 400L unvented would suffice for 10 showers running at the same time. However you then need the recovery time if they are used straight after.
You will be looking at a big breaker tank feeding a booster pump/pumps.
Definitely. That's what I thought it would be good to get a manufacturer out to spec it. Thought Stuart Turner did this and was wondering what others. Shaun has suggested DAB