Hi, 1st question from a newbie. I've had a search & can't find a thread on this.

I have a worcester bosch greenstar boiler with 17 rads.
I have a EasyControl with 14 of the rads having Bosch eTRVS. I do not use the weather compensation settings.
I have a couple of queries if anyone has set up a similar system.
1. The system has an autobalance feature. If I use this should I fully open the lockshields?
2. On occasion the rads with no trvs (in bathrooms) do not heat the rooms fully. I think maybe because the system is modulating the boiler as the rest of the zones hit target temp. So should I set one zone deliberately high to ensure the boiler stays on or is there a better way to finness this?

Thanks for your help.
 
Hi, I would probably try running the rads a bit hot when balancing but if they're undersized or rooms are a bit draughty then this may not solve.
Why have you left just these three rooms without heads?
 
Hi, I would probably try running the rads a bit hot when balancing but if they're undersized or rooms are a bit draughty then this may not solve.
Why have you left just these three rooms without heads?
Hi, I would probably try running the rads a bit hot when balancing but if they're undersized or rooms are a bit draughty then this may not solve.
Why have you left just these three rooms without heads?
Hi thanks appreciated, the ones without heads are in bathrooms & 2 do have normal TRVs but 1 is also a wet room & I was concerned about having a smart TRV in case it gets wet. All the other rads have smart TRVs.
Question 1 was more about using the autobalance feature on the EasyControl.
 
I've not used autobalance but I guess it adjusts valves based on how fast they reach desired temp. I guess it would work well aslong as lockshields aren't closed too much but I'd be sceptical about just relying on that and wouldn't ignore balancing completely.
Smart heads should be fine except in wet room so I'd just leave that one without.
 

Reply to Bosch EasyControl & autobalance in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
288
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
211
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
284
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
499
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
367
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock