Paddy57

Messages
4
Hi, 1st question from a newbie. I've had a search & can't find a thread on this.

I have a worcester bosch greenstar boiler with 17 rads.
I have a EasyControl with 14 of the rads having Bosch eTRVS. I do not use the weather compensation settings.
I have a couple of queries if anyone has set up a similar system.
1. The system has an autobalance feature. If I use this should I fully open the lockshields?
2. On occasion the rads with no trvs (in bathrooms) do not heat the rooms fully. I think maybe because the system is modulating the boiler as the rest of the zones hit target temp. So should I set one zone deliberately high to ensure the boiler stays on or is there a better way to finness this?

Thanks for your help.
 

Knappers

Plumber
Gas Engineer
Messages
981
Hi, I would probably try running the rads a bit hot when balancing but if they're undersized or rooms are a bit draughty then this may not solve.
Why have you left just these three rooms without heads?
 

Paddy57

Messages
4
Hi, I would probably try running the rads a bit hot when balancing but if they're undersized or rooms are a bit draughty then this may not solve.
Why have you left just these three rooms without heads?
Hi, I would probably try running the rads a bit hot when balancing but if they're undersized or rooms are a bit draughty then this may not solve.
Why have you left just these three rooms without heads?
Hi thanks appreciated, the ones without heads are in bathrooms & 2 do have normal TRVs but 1 is also a wet room & I was concerned about having a smart TRV in case it gets wet. All the other rads have smart TRVs.
Question 1 was more about using the autobalance feature on the EasyControl.
 

Knappers

Plumber
Gas Engineer
Messages
981
I've not used autobalance but I guess it adjusts valves based on how fast they reach desired temp. I guess it would work well aslong as lockshields aren't closed too much but I'd be sceptical about just relying on that and wouldn't ignore balancing completely.
Smart heads should be fine except in wet room so I'd just leave that one without.
 

Paddy57

Messages
4
Thanks for this, much appreciated.
Hi just in case someone has the same question. I had a response from Bosch tech support. They say yes for best results on Autobalance fully open lock shield on all rads with smart TRVs fitted.
 

Reply to Bosch EasyControl & autobalance in the Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar threads

D
It’s sometimes is air but half of the problem is it’s flow noise / turbulence around the centre of the magnet it should go away after a week etc...
Replies
1
Views
101
ShaunCorbs
ShaunCorbs
B
The only product I can find is: BWT AquaDial Combi-Care Compact 15 mm scale inhibitor (AC002100). I'm assuming this would be compatible with a...
Replies
3
Views
399
Bob Fleming
B
IanHoll
Replies
10
Views
2K
ShaunCorbs
ShaunCorbs
Zig168
Those LCD panels look spot on and better than the similar priced Honeywell ones on Amazon.
Replies
5
Views
236
Zig168
Zig168
Inverness
Zone 1 does the whole house including upstairs. Zone 2 only does the master bedroom. The house size is less than 150sqm more like 100sqm. It's...
Replies
10
Views
592
Inverness
Inverness
Creating content since 2001. Untold Media is a Registered Trademark.

Newest Threads (Please Reply)

Search Forum

Top