problem with my oil boiler everything has been change all cleaned out set up but still locks out , if I remove photcell and shine a light on it it runs fine replace photocell and it stops again , new cell and control box, heating engineer is beat now as well
 
Might be seeing a false flame, to test, keep light shining on the removed photocell before trying to fire up, it should lockout and not fire up.
Make of boiler/burner?.
 
cell works exaclty as it should when out but locks out everytime when in position grant vortex 16/21 riello burner
All oil boilers check for a stray/false flame before allowing the boiler to fire up, so if you have the cell out and you have a light shining on it before you press the start button then it shouldn't fire up, can you check this out.
To fire up with the cell removed, it has to be covered during the purge period which on my 17 year old Firebird (Riello G5X burner) is 12 secs, the ignition transformer is then energised and the solenoid opens the oil valve and a flame must be detected within 5 secs, so if you shine the light on it after 12 secs it may light up and allow the burner to continue firing, For safety reasons you obviously don't keep it running in this fashion, as soon as you remove the light or blind the cell then the burner should trip with the combustion failure light illuminated.
 
Does it have a flame diffuser? Original problem could have been a spot clogged diffuser, which is now clean but has been reinstalled upside down. His prevents the light getting to photocell.

This is not specific to your boiler/I don’t know what the diffuser looks like on your boiler but have come across this before on bigger Riellos.
 

Reply to boiler locks out , complete service and parts change in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
241
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
161
P
  • Question
Boiler is SIRIUS THREE FS 70 Potterton commercial. Situation: We are small building contractors and my labourers managed to damage the radiator pipes during the strip out. Not the end of the world as damages happens. I am responsible builder and paying my bills and to repair the damages if...
Replies
2
Views
61
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
293
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
504
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock