problem with my oil boiler everything has been change all cleaned out set up but still locks out , if I remove photcell and shine a light on it it runs fine replace photocell and it stops again , new cell and control box, heating engineer is beat now as well
 
Might be seeing a false flame, to test, keep light shining on the removed photocell before trying to fire up, it should lockout and not fire up.
Make of boiler/burner?.
 
cell works exaclty as it should when out but locks out everytime when in position grant vortex 16/21 riello burner
All oil boilers check for a stray/false flame before allowing the boiler to fire up, so if you have the cell out and you have a light shining on it before you press the start button then it shouldn't fire up, can you check this out.
To fire up with the cell removed, it has to be covered during the purge period which on my 17 year old Firebird (Riello G5X burner) is 12 secs, the ignition transformer is then energised and the solenoid opens the oil valve and a flame must be detected within 5 secs, so if you shine the light on it after 12 secs it may light up and allow the burner to continue firing, For safety reasons you obviously don't keep it running in this fashion, as soon as you remove the light or blind the cell then the burner should trip with the combustion failure light illuminated.
 
Does it have a flame diffuser? Original problem could have been a spot clogged diffuser, which is now clean but has been reinstalled upside down. His prevents the light getting to photocell.

This is not specific to your boiler/I don’t know what the diffuser looks like on your boiler but have come across this before on bigger Riellos.
 

Reply to boiler locks out , complete service and parts change in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
365
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
212
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
301
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock