new cell fitted and still the same , chamber all cleaned, new nozzle and good sparkI’m not an oily, but if it works when you apply light, I’d be looking in that area. Either faulty photo cell or not enough light?
grant vortex 16/21 riello burnerYep, give us an idea of the boiler and burner.
Need a new boiler man as well if they're stuck with this.
cell works exaclty as it should when out but locks out everytime when in position grant vortex 16/21 riello burnerMight be seeing a false flame, to test, keep light shining on the removed photocell before trying to fire up, it should lockout and not fire up.
Make of boiler/burner?.
cant answer that has boiler man has given up and leftWhat co2 and excess air is it running at?
grant helpline say its a combustion issue but when we trick it to go it burns well fires up lovely and runs finegrant vortex 16/21 riello burner
All oil boilers check for a stray/false flame before allowing the boiler to fire up, so if you have the cell out and you have a light shining on it before you press the start button then it shouldn't fire up, can you check this out.cell works exaclty as it should when out but locks out everytime when in position grant vortex 16/21 riello burner
Grant are correct, it won't be fixed without the correct equipment.grant helpline say its a combustion issue but when we trick it to go it burns well fires up lovely and runs fine