lambchop

Joined a firm who does solar thermal & PV, so a newbie at the green stuff

As above it was an oppen vented cylinder + solar therm + boiler. The experienced Installer who Im working under wanted me to fit the TMV on the hot outlet of the cylinder before the open vent pipe. I was confused at first thinkig it was some sort of test, I pointed out that the TMV needs to be on the other side of the open vent otherwise it becomes a sealed system.

He went a bit pale then, Am I right, I think I am. I done a post before about system working pressure and the charge on the expansion vessel being different. Will pay for the BPEC course myself if I have to as I dont mind working under someone but Im getting conflicting info all the time
 
A TMV should be fitted after the open vent as you say, did it not have instructions? A typical installation can be seen on page 2 here
 
Sounds like there may be a few dodgy installs out there if he went a bit pale when you pointed out the error in his ways :)
 
On the plus side tho, at least a vented cylinder will prob only take a wall out if it bursts; unvented takes much much more.
 
no mate, I always take a little time out to read m.i's while having a coffee. The guy I was working under took the mick that he could tell that I was trained up by reading books!!!! wtf! I know a little but I dont know everything so always keen to learn. Installer = trained to install products, whereas Plumber = Installs but knows the science behind the installation
 
Agree. As is often said, if all else fails read the instructions.
The person that reckons they know it all knows *** all.
 
My fave RTFB = Read The F'ing Book, got to go missus is getting irate, time for a beer, a bit of face stroking and watch True Blood
 
If the valve is in the wrong place on the vent pipe it wouldn't blow up, the cold feed to the cylinder is also effectively open vented, so the expansion would go up this pipe instead.
 
If the valve is in the wrong place on the vent pipe it wouldn't blow up, the cold feed to the cylinder is also effectively open vented, so the expansion would go up this pipe instead.
Ar' but without an effective "safety open vent pipe" you are required under Building Regs G to install a Temperature relief safety valve !!!! just like an un-vented.
 
Status
Not open for further replies.

Reply to Blending valves on a open vented cylinder... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I was hoping to replace an old system boiler with a Vaillant Ecotec Exclusive 627 system boiler, thats the one with the diverter valve so no...
Replies
1
Views
179
Hi, I'm new to the forum and just some background on myself. I have 4 years experience as a plumber but haven't worked in the trade in 15 years. I...
Replies
13
Views
630
    • Funny
Hi guys, I have a question regarding converting an open vent system (copper cylinder) to pressurized, reason being not enough drop from the loft...
Replies
13
Views
1K
Hello, I am renovating a small bathroom in an apartment on the 5th floor. Heating is electric, no gas or oil. I have four (related) questions...
Replies
1
Views
779
Hi all. As the title says, I have a problem with an unvented cylinder I had installed last year where the first time I turn a hot tap on after the...
Replies
27
Views
2K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock