I’ve got a 6 bedroom house with 4 bathrooms. There are 24 radiators in total. It’s a sealed system with an expansion vessel.

I’m going to upgrade the existing Grundfos pump to a small commercial type. I’ve already got two pumps in my possession to choose from. The Grundfos UPS2 25-80 and the Grundfos Alpha2 25-80. I’m looking for opinions on which pump to use or in fact if you think that neither of them are a good choice.
 

Attachments

  • CA606ED8-CE1D-426F-BACC-B16F0B554C04.jpeg
    CA606ED8-CE1D-426F-BACC-B16F0B554C04.jpeg
    78 KB · Views: 17
  • 8D214C0D-BD11-449F-BDFA-FFEB01D938FC.jpeg
    8D214C0D-BD11-449F-BDFA-FFEB01D938FC.jpeg
    69.1 KB · Views: 17
Ups2 25-80 haven’t had any problems with them but depending on controls you might need a relay (due to amp draw)
 
According to Grundfos Product Centre the UPS2 15-50/60 has been replaced by the UPS3 15-50/65. The UPS2 25-80 and UPS2 32-80 are still available.
[automerge]1574855265[/automerge]
I’ve got a 6 bedroom house with 4 bathrooms. There are 24 radiators in total. It’s a sealed system with an expansion vessel.

I’m going to upgrade the existing Grundfos pump to a small commercial type.
Why?
 
Last edited:
I'm sure if you share what area you are from (only thereabouts, don't need to share entire address of course) then there may be a member on here that can help.

I’m in Reading, Berkshire
[automerge]1574879190[/automerge]
According to Grundfos Product Centre the UPS2 15-50/60 has been replaced by the UPS3 15-50/65. The UPS2 25-80 and UPS2 32-80 are still available.
[automerge]1574855265[/automerge]

Why?

The manufacturer’s installation instructions for my boiler suggest using a small commercial pump. British Gas engineer told me that using a standard pump can lead to premature failure of the heat exchanger.
 
It’s a Potterton Suprima 120L
That's very useful.

The Suprima 120L is a 35kW boiler so the required flow rate at an 11C temperature drop is approx 46 litres/min or 2.76 cu.m/hr; the pressure drop across the boiler is 1.2m.

Looking at the pump curve for the Alpha2, the pump can only produce 3.2m head at 2.76 cu.m/hr, on speed 3. So this leaves only 2m for the heating circuit (3.2 - 1.2), which willl not be sufficient.

The UPS2 25/80, on the other hand, can produce between 5m and 8m head at 2.76 m.cu/hr, depending on speed, leaving between 3.8m and 6.8m for the heating circuit. which should be adequate.
 
Last edited:
That's very useful.

The Suprima 120L is a 35kW boiler so the required flow rate at an 11C temperature drop is approx 46 litres/min or 2.76 cu.m/hr; the pressure drop across the boiler is 1.2m.

Looking at the pump curve for the Alpha2, the pump can only produce 3.2m head at 2.76 cu.m/hr, on speed 3. So this leaves only 2m for the heating circuit (3.2 - 1.2), which willl not be sufficient.

The UPS2 25/80, on the other hand, can produce between 5m and 8m head at 2.76 m.cu/hr, depending on speed, leaving between 3.8m and 6.8m for the heating circuit. which should be adequate.

Thanks for your detailed response.
 
That's very useful.

The Suprima 120L is a 35kW boiler so the required flow rate at an 11C temperature drop is approx 46 litres/min or 2.76 cu.m/hr; the pressure drop across the boiler is 1.2m.

Looking at the pump curve for the Alpha2, the pump can only produce 3.2m head at 2.76 cu.m/hr, on speed 3. So this leaves only 2m for the heating circuit (3.2 - 1.2), which willl not be sufficient.

The UPS2 25/80, on the other hand, can produce between 5m and 8m head at 2.76 m.cu/hr, depending on speed, leaving between 3.8m and 6.8m for the heating circuit. which should be adequate.

Out of curiosity, how did you determine the flow rate was 46 litres/min?
 
From the installation manual (actually shows 45.82); but it's easy to calculate.

litres/min = (60 x kW output) /(4.18 x ΔT) where 4.18 is Joules Constant, and ΔT is the difference between flow and return temperatures.

I should have said 46 litres/min assumes the boiler is set to "Winter". If it's set to "Summer" the flow is approx 31 litres/min.
 
From the installation manual (actually shows 45.82); but it's easy to calculate.

litres/min = (60 x kW output) /(4.18 x ΔT) where 4.18 is Joules Constant, and ΔT is the difference between flow and return temperatures.

I should have said 46 litres/min assumes the boiler is set to "Winter". If it's set to "Summer" the flow is approx 31 litres/min.

Thanks again for your informative response.
 

Reply to Best choice out of 2 Pumps in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hi, some professional advice would be greatly appreciated, We are having an Unvented Cylinder installed into our 2 bedroom ground floor flat. I...
Replies
17
Views
9K
S
  • Locked
Hi All, First post here and I'm hoping for some assistance to quell my worries and let me have a good night sleep. Before I start, I would...
Replies
2
Views
685
scottiecb19
S
  • Locked
I have been asked to enquire about various options for a job where the customer is going to install a portable toilet block at a local social...
Replies
7
Views
1K
Dotty
D
  • Locked
Scenario: 3 Bedroom 1970’s bungalow 110m2 - off gas main. Run as self catering holiday let in South Devon. Suspended timber floor. Loft well...
Replies
21
Views
3K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock