Gray0689
???
1600 square feet = 149 square metres.
Or am I misunderstanding you?
House is 6500 square foot ray
500litre cylinder
6 manifolds
7 towel rads
Discuss Advice needed. Issues with underfloor heating and hot water system for new build in the Plumbing Jobs | The Job-board area at PlumbersForums.net
???
1600 square feet = 149 square metres.
Or am I misunderstanding you?
House is 6500 square foot ray
500litre cylinder
6 manifolds
7 towel rads
A low loss header would of been good for that set up
But to be honest I would be thinking the plumber made a hash of that as pipework is undersized
Another good job ruined by cutting corners imho
Heat loss calcis have been done to size the boiler to the heat output required, indicating the boiler is oversized by about
Reply to Advice needed. Issues with underfloor heating and hot water system for new build in the Plumbing Jobs | The Job-board area at PlumbersForums.net