Discuss Baxi 100 HE overheats and melts heat exchanger - an explanation in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
T

TheGasEngineer

Overheating Baxi 100 HE condensing boiler.

First of all switch that boiler off. It's DANGEROUS!! read on...

If you have met a Baxi 100 HE with a melted combustion chamber it’s caused by perished glue allowing the burner ceramic to lift and cause furnace-like volumes of gas/air mixture to enter the combustion chamber.


The ceramic face only becomes loose when it gets hot. When it does become loose it lifts and the fan responds by pumping a vastly greater volume of gas/air mixture into the combustion chamber. For the boiler I have just been investigating the working pressure dropped 3mb which indicates the increase in gas rate. I couldn’t measure the gas rate at the meter because it had overheated well before I could get there.

What seems to happen is the glue begins to fail and little by little the ceramic lifts - maybe over several weeks. So the boiler starts to run hot and I guess this contributes to the failure of the manifold O-ring and maybe even the flow switch. If you think about it, if there is overheating, it must be excess gas. It can't be anything else. The problem is that once the boiler shuts down the ceramic drops back onto its seat, the glue solidifies and amazingly it looks to all intents and purposes like a perfectly serviceable component.

The boiler overheats enough to melt and distort all the lower parts of combustion chamber aluminum and wreck the door seals - it cinders them. Then it overheats and shuts down usually via the fan stat. On stopping, the ceramic then drops back into the metal burner base. When it’s cool enough to handle the ceramic it's held rigidly in place again, sitting there all innocently.

About a year ago I was called to a 100HE and the sump of the
combustion chamber and 2 to 3 inches of the lower side walls had melted. It was a mess. I couldn’t think how sufficient gas had entered the combustion chamber to get so hot. Of course the ceramic element was sitting there looking secure in the pressed steel base.

A 100HE kept me baffled for a week. The flow switch had failed and the lower manifold was leaking just to add to the confusion. When to door came off the seals had gone but not cindered. I fitted new ones and left it running. This time it seriously overheated and melted the sump base. I thought I had not put the seals on properly causing the overheat. I talked to Baxi technical but they hadn't a clue. With a new base, flow switch and manifold O-ring in place the boiler overheated again (Arrrrgh!!). It quickly became red hot inside and it roared noisily. I didn't know what the roar was. There was some damage but not too much and so I ran it up again and watched very carefully. Initially the flame looked as it always had from cold - blue and fairly quiet (almost normal). And then bit-by-bit it started to roar and the internals of the combustion chamber turned cherry red. Then in an instant as it was really overheating I happened to see the ceramic lift. I couldn’t believe it at first but then it stuck half out and when it cooled down there it was, jammed solid but at an angle and finally revealing the problem.


I find it shocking that Baxi haven't recognised this fault. From what I see there are multitudes of these boiler breaking down like this and they could be salvaged just by replacing the burner every three years. It just needs Baxi to admit it and put out a general warning. I think a warning is necessary because it's a fire-bomb waiting to happen.

I rang Baxi tech support and really pressed them about the excess heat and they didn't have a clue. There was not one suggestion or offer of help or any interest at all. I told him about the low working pressure and he said this would seriously affect the performance of the gas valve. Rubbish!! Actually this is where the zero governor is a pain - as soon as the flow restriction of the ceramic was lowered (when the ceramic lifted off its seat) the flow rate through the fan rose exponentially and the valve just increased the flow of gas to match resulting in an inferno in the combustion chamber. If that is not a design fault then I don't know what is...

So if you service the Baxi 100 HE range (or any boiler that uses that burner) I suggest it's replace every third service.
 
I think is the overriding issue with this burner is when it's in a boiler with a 1:1 govenor in particular there is the potential for furnace-like conditions that destroy the boiler. There should be a national recall or compulsory refurb. A fault that can cause and aluminium block to melt is dangerous beyond belief. The only thing between the property and an inferno is the fan stat.

When the ceramic lifts, there is obviously a significant drop in burner flow resistance and the fan responds by pumping a vast increase in air. And the 1:1 valve responds likewise to give a perfect gas / air mixture, resulting in a furnace.

It must be feasible to add a function to the pcb that detects a drop in load on the fan and shuts it down and prevents it lighting.
 
That's a good idea. I could dress and present like Sir Patrick Moore -loads of arm waving and squinted looks - and maybe a garage demonstration of the burner turning into a flamethrower ... Boom... LOL :)
 
I had the same problem but i saw the burner lifting
before any damage was caused - Just the noise was a worry. I know it doesn't comply but a little fire cement around the edge of the ceramic burner has been enough to hold it in position and stop the explosion on start up.
 
so whats the answer to this new burner ? as i have been to view baxi combi 80 he plus tonight and it is giving off same faults - explosive ignition, and then when it does light the boiler ramps up and gets to point that i need to stop fan goes louder and flames more fierce.
 
so whats the answer to this new burner ? as i have been to view baxi combi 80 he plus tonight and it is giving off same faults - explosive ignition, and then when it does light the boiler ramps up and gets to point that i need to stop fan goes louder and flames more fierce.
change the boiler its useless and i wont fit the solo HE or work on one ever
 
so whats the answer to this new burner ? as i have been to view baxi combi 80 he plus tonight and it is giving off same faults - explosive ignition, and then when it does light the boiler ramps up and gets to point that i need to stop fan goes louder and flames more fierce.
If your boiler has the burner with a ceramic plate or the old one with the cloth-like burner that pulls lose and allows more combustion mixture into the combustion chamber, then you with get lots of combustion problems. In order to explain such a problem it is a case of relying on what we know about boilers. We know that a centrifugal fan and 1:1 gas valve will deliver massive quantities of combustion mixture if allowed to run unrestricted with no back-pressure. We know the burner with a glued-in ceramic will start to lift after a couple of years and provide an unrestricted pathway for the combustion mixture. All you have to do is light it, stand back and watch the boiler become a furnace.

If the burner is replaced it can't overheat, Of course there may be other problems nevertheless, but overheating will not be one of them.
 
i'll check today, to be honest i was looking at gas valve and a stat problem before i come across this and now this explains exactly whats happening cheers :)
 
I thought it was the gas valve to start with. I was lucky to see the ceramic move as the thing overheated. It was a one in a million chance that I saw the movement. It took me a couple of months of contemplation after that before I realised the implications and could formulated a coherent explanation.

The difficulty is that after a boiler has overheated and switched off, the glued-in ceramic cools off, solidifies and looks perfectly OK. So even in a bad overheating incident there would be no reason to suspect the burner. I have not had so much experience with the older burner with the cloth-like, or fibrous element, but the one I have seen had very poor seals around the edge where it was bedded into the pressed steel burner base.

In my opinion this is manufacturing and design fault. After a fair bit of investigation I realised there is no national authoritative body to report issues like this. The Gas Safe Register can't help, and as many of their staff where employed by the large boiler manufacturers, one could be forgiven to think they are there to suppress any bad press about their old employers products. The Fire Brigade can't help and the HSE want someone to die before they will get out of bed. After reporting it to my MP it did get as far as the Baxi's CEO but off course he said it is fine, and my MP believed him!

I would love to get hold of a set of pictures of melted heat exchangers from this range of boilers so that I could re-start my campaign to force Baxi to start a national repair process. There was a picture in the September Gas Engineer but despite numerous attempts at contacting the contributor, he would not respond.

I would be interested to know how you get on. Could you provide the boiler CG number please?
 
I thought it was the gas valve to start with. I was lucky to see the ceramic move as the thing overheated. It was a one in a million chance that I saw the movement. It took me a couple of months of contemplation after that before I realised the implications and could formulated a coherent explanation.

The difficulty is that after a boiler has overheated and switched off, the glued-in ceramic cools off, solidifies and looks perfectly OK. So even in a bad overheating incident there would be no reason to suspect the burner. I have not had so much experience with the older burner with the cloth-like, or fibrous element, but the one I have seen had very poor seals around the edge where it was bedded into the pressed steel burner base.

In my opinion this is manufacturing and design fault. After a fair bit of investigation I realised there is no national authoritative body to report issues like this. The Gas Safe Register can't help, and as many of their staff where employed by the large boiler manufacturers, one could be forgiven to think they are there to suppress any bad press about their old employers products. The Fire Brigade can't help and the HSE want someone to die before they will get out of bed. After reporting it to my MP it did get as far as the Baxi's CEO but off course he said it is fine, and my MP believed him!

I would love to get hold of a set of pictures of melted heat exchangers from this range of boilers so that I could re-start my campaign to force Baxi to start a national repair process. There was a picture in the September Gas Engineer but despite numerous attempts at contacting the contributor, he would not respond.

I would be interested to know how you get on. Could you provide the boiler CG number please?

Jesus thanks for the info pal, got an iffy HE133 which may have this problem, its rarly used in an industrial unit so i am awaiting if he wants a repair or a shiny WB
 
the burners are expensive not worth doing as gas man said change the boiler from memory £160 then gasket kit on top
 
The only way of stopping thermal runaway of those BAXI fireboxes would be by restricting the gas flow by gas isolator/service cock (partially closed) before the boiler (or fitting a suitable in-line orifice), so it can't maintain 1:1 air/gas ratio on high outputs (above rated power).
This way it wouldn't overheat, because there would be no enough gas, even when the ceramic takes off...
The only cons would be a slight efficiency loss on a max output.
Of course the combustion chamber can still be damaged, if the flame is directed to one side of it.

As to me, this is major design flaw: why the governor allows more gas in than the rated boiler input? Especially when the insides of it are made from alluminium, and quite often it has a PLASTIC flue?
If it has been lined with a firebricks (or at least had a thick cast iron combustion chamber), with stainless steel flue, than it shouldn't have ever melted...
The only explanation for governor, is that thay use the same part in a higher rated boilers, and DIDN't even bother fitting a correctly sized orifice before governor...

I think after a few heavy fire damage insurance claims caused by those BAXIs, there would be a national recall/refurb of those boilers. At least they can try fixing the ceramic grill by tying it down by the nichrome/tungsten/(heater) wire.
PS: Only for experienced gas safe persons, with practical burner design experience.
 
Status
Not open for further replies.

Reply to Baxi 100 HE overheats and melts heat exchanger - an explanation in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock