Is a 24kw big enough for 9 rads
Discuss Not all Rads getting hot in the Plumbing Jobs | The Job-board area at PlumbersForums.net
It is an end of terrace with high cielings.It has a cellar which I have put rock wool between joists and boarded so the lounge does not get the cold from below.
24 KW combi or system boiler ????
Has the pump been checked? The fast temperature rise could be due to a faulty pump, which could be the reason for the very hot pump. In any case the pump is installed incorrectly as the shaft should always be horizontal, not vertical as in your pics. The installer should have drawn this to your attention.He isolated the C/H circuit & found restriction in boiler or coil.Temp rises fast on boiler 49 degrees cent to 74 degrees in 40 seconds 9Been told this could be blockage in the heat exchanger )
The casing on the C/H circ pump gets that hot I cant hold my fingers on it.
This is only true if they are one-direction TRVs. If they are modern bi-directional TRVs it doesn't matter which end they go. Look on the metal body of the TRV for one or two arrows. If there is only one arrow the TRV must be installed so the arrow shows direction of flow (towards rad on the flow - hotter pipe, away from rad on return - cooler pipe). It there are two arrows at 90 degrees, it's a bidirectional TRV and can go on either end.2 rads have TRV's at wrong end.