Discuss Worcester Bosch Green Star combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

fubar1000

Gas Engineer
Messages
199
Morning all

Had a call from a custard a couple of weeks ago about the above making a funny noise

To cut it short, when I got there the condense trap & internal condense hose was full with black grit.

Cleaned it all out & boiler was working fine.

Had another call yesterday about the same thing, so I flushed it all & boilers was working fine when I left.

But it looks like it could be coming from the heat exchanger.

Anyone had this before????

Thanks peeps
 
Is it the bean tin heat exchanger? Might need cleaning out or replacing? Fins might be disintegrating?
 
They do get a lot of grit in them, if the trap has never been emptied it could have backed up.
 
I'm not sure what heat exchanger is in it tbh, but it seems to be a bit like the grit found inside the central heating system / rads

Boiler seems to run fine

Thanks
 
Check the FGR and the fan pressure is as MI's fubar1000. Also gas pressure/gas rate. I don't get to work on that many but knowing the basics are ok at least rule out the obvious regards flame and flue function yeh? :)
 
Yes if it's the older one (possibly BG rebrand) hex cream crackered. Take of front of burner (alu plate on front of burner.) if it's brown and full of silt just sell them a new boiker.

If it's the SI (kebab) get service kit. If the burner feels like a tin of beans when you run hand down side ........ Walk away. Slowly and then break into a sprint towards your sales literature
 
Status
Not open for further replies.

Reply to Worcester Bosch Green Star combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
296
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
477
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
232
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16...
Replies
0
Views
246
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
563
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock