Good afternoon all,

I have a Worcester boiler installed recently. It was moved from the first floor to the loft. Existing 22mm condense pipe was extended to the loft. It looks like the old pipe has no slope and prevents air to get into the boiler condensate trap, preventing condensate to drain. After the pipe is blocked, when the engineer removed the boiler connection, the pipe sucked air and started to drain immediately.

The installer offers me a pump or replacing the old section which would mean a lot of work such as lifting the floorwoods, breaking the tiles etc. My proposal was to install an air admittance valve on the PVC condensate drainage. The pipe will suck air from the AAV and push the water with gravity (almost 3m fall). Please see the sketch drawing of the system. attached.

In theory, it should work, however, have you had any similar issues? Have you got any advice on the issue?

Thank you very much in advance,
 

Attachments

  • Boiler.png
    Boiler.png
    102.4 KB · Views: 9
Your diagnosis and proposed remedy seem wrong to me. Air should get down into the trap down through the boiler not up from the outlet. You must have a blockage somewhere. Possibly a temporary block installed for the move that was forgotten about.

It a registered 'Gas Safe' engineer to find and fix the problem for you. Don't be tempted to DIY.
 

Reply to Worcester boiler condensate won't drain. in the USA area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
265
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
65
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
245
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
189
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock