T

Tom_B

Hi Everyone,

My CH system has a an underfloor heating loop in the kitchen. What I want to do is run the UFH 24 hours with its own control system. The Glow worm 38cxi boiler only has one circulation pump so can I fit a motor valve into the radiator circuit and control it with a wireless thermostat? Is there enough of a loop that the circulation pump will be ok or will bad things happen?

I have attached a picture of the boiler layout.

thanks!

Tom
 

Attachments

  • IMG_0102.JPG
    IMG_0102.JPG
    650.1 KB · Views: 24
Hi Tom, your Gloworm has its own internal circulator pump and the ZRU of your UFH also has its own circulator pump. So you can have two separate zones by installing a motorised valve and a room thermostat. Just make sure you also include a differential automatic bypass as well and it won't blow up.
 
Hi Darren,

Thanks for your reply, so the differential bypass valve would go in just before the motor valve and bridge the flow and return pipes?
 
Brilliant - thanks Darren, I guessed something like that would be necessary, your help is much appreciated.
 
Status
Not open for further replies.

Reply to Will doing this blow up the heating system? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We have a three zone heating system plus water cylinder (OSO Super S 250L) on an Valliant EcoTec 637. Two CH zones and a UFH zone. Boiler is...
Replies
3
Views
265
Hi, I am replacing our 11 year old boiler (due to H.Ex. leak) with a new one. This is in a "sealed" system with red expansion vessel in airig...
Replies
3
Views
553
Hi All, Looking for a bit of advice on the best way to pipe this. - 24kW Worcester regular boiler in kitchen, approx. 9 years old - unvented...
Replies
16
Views
1K
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem...
Replies
9
Views
403
  • Question
Hello, I have a gas boiler in my apartment that heats a net area of 300 m2 with an underfloor heating system. The boiler has a capacity of 45 kW...
Replies
3
Views
456
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock