Hello Everyone,
My first post hope I don't break any rules! but I am seeking advice on my wet under floor heating system which is about 6 years old in a new build of that age.
The system comprises of Camray 5 external oil fired boiler, circulating pump mounted on the boiler, basic temperature control also on the boiler.
Megaflo unvented mains pressure water heater with Honeywell 2 port valve on the primary circuit pipe, cannot find any other one.
7 zones, 4 downstairs and 3 upstairs each with digital 7 day thermostats which all appear to click on display correctly and demand heat.
Each zone has an actuator valve showing red.
New ufh circulating pump fitted correctly and confirmed as working.
Boiler responding to demand for HW but not for UFH.
Hot water present to one side of the pump and the mixer valve.
System pressure and temp OK.
It would seem that the heat call from the thermostat to the pump and the actuators is not operating the pump and opening the actuators.
This system has worked without fault until the pump failure which has been bled etc.

Could anyone with the knowledge of these systems suggest any way forward please?
NB. I have just discovered that there is no mains supply showing at the back of each thermostat is this the obvious problem or am I missing something else?
 
Yes if no power at stats then the heating won't come on to underfloor side as actuators won't open sounds like you have a fuse blown or a faulty wire somewhere
 
some systems dont have high voltage at stats need to know what system
 
Thank you all for the replies.
I think the system was constructed on site by a contractor using commonly available parts.
The thermostats are powered by dry batteries the rear contacts of which seem to go into electrical mains voltage wires
,thence to the terminal board where they contact with mains driven actuators which are marked 240v.
Having checked the security of the wires in the terminal box I can establish mains power from the breaker to the isolator switch and then to one terminal block in the box.
Since doing this one of the actuators shows open and the terminal shows 240v but the pump does not operate.
If I independently power the pump that zone heats and the respective thermostat will provide power to the terminal but won't operate the actuater.
Detaching each actuator does not replicate this situation with them.
Mystery!!!
 
Actuators showing RED mean they are not open letting thus not letting any heat through. it is extremely rare for all the actuators to not work so there is a problem somehwere. Remove all actuators (they should unscrew) this should let water flow to all zones. You need an electrician in to see where the link is broken and to check everything is wired correctly. You may need a replacement wiring centre
 
post some pics and makes it easy to identify. have you checked the zone valve on the ufloor manifold some have them some dont
 
Thank you all for your replies to my queries. Having spent the last couple of days with the meter in the two terminal boxes, one by the downstairs 4 zone manifold and one upstairs by the 3 zone manifold, I have at least established the wiring setup.
I still cannot get the pump to run if any one of the thermostats call.
I cannot get any zone valve to open via the thermostat calling except 1 zone, which shows 240v at the thermostat when calling for heat.
All others show closed.
This system does not have a wiring centre but has two terminal boxes as above.
There is switched power to the downstairs box but the only power to the upstairs box seems to come from the megaflo cylinder connections.
I have attached a couple of pictures if they prove to be any use.
Probably have to look up an electrician shortly.
 

Attachments

  • 20120111_0436.jpg
    20120111_0436.jpg
    89 KB · Views: 22
  • Heating wiring.jpg
    Heating wiring.jpg
    98.5 KB · Views: 18
  • 20120111_0437.jpg
    20120111_0437.jpg
    85.1 KB · Views: 19
  • Heating wiring 001.jpg
    Heating wiring 001.jpg
    92.2 KB · Views: 15
  • 20120111_0435.jpg
    20120111_0435.jpg
    90.2 KB · Views: 17
Looks like the boiler circuit is vented and the uf sealed and the plate is transferring between the two.
 
Status
Not open for further replies.

Reply to Under Floor heating failing to start. Advice needed in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
137
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
231
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
202
P
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock