Hello everybody! I just need professional advice from you guys as i have never seen something like that before. In bathroom under the sink there is two isolation valves, they are about 400 mm above the floor level.Client wants to install vanity unit with basin which will make isolation valves inaccessible.
My question: Is it good practice(allowed) to install isolation valves inside vanity cabinets for easy access, and leave those two that will be inaccessible on the same supply? or its have to be only 1 isolator on the same supply?

Thank you for your advices.
 
A photo would have been helpful. Good practice and being allowed are 2 different things. Isolation valves are good practice, but not required. Any isolation valve that is required, must be accessible, such as a stopcock, an isolation valve for a cold water storage cistern.
 
A photo would have been helpful. Good practice and being allowed are 2 different things. Isolation valves are good practice, but not required. Any isolation valve that is required, must be accessible, such as a stopcock, an isolation valve for a cold water storage cistern.
 

Attachments

  • 7B32DCDB-DC3E-4E99-9400-EA470D8A777B.jpeg
    7B32DCDB-DC3E-4E99-9400-EA470D8A777B.jpeg
    512.6 KB · Views: 34
  • A5948C99-3662-4FBF-8A17-C80E975F60DF.jpeg
    A5948C99-3662-4FBF-8A17-C80E975F60DF.jpeg
    190.7 KB · Views: 32
A bit on the low side, but small bore isolation valves, so any additional ones could reduce performance of the taps. Is it not possible to remove them, extend the pipework and then refit them?
 
Best to remove and extend with soldered couplings and depending on the vanit unit yes install new iso valves don’t reinstall the old ones
 
Is it not possible to remove them, extend the pipework and then refit them?
Its a bit low to solder them, specially the valve on the left,at least i can use compression coupler to extend the pipes. thats why i am asking if i add another two isolation valves inside vanity.
 
Its a bit low to solder them, specially the valve on the left,at least i can use compression coupler to extend the pipes. thats why i am asking if i add another two isolation valves inside vanity.
That’s fine to solder. I wouldn’t be putting compression joints in a place you can’t access.

What happens in 6 months when one of the joints has a leak. Gonna tip out the new unit to get to it?

Remove existing valves, pull olives/nuts, solder coupling and new pipe. For ease, can even use a solder ring coupling.

Edit: For peace of mind, wet the floor/area before soldering.
 
Thank you very much for your help guys.
I've found this sort of thing useful in that situation (if there's room to get it in!)
 

Reply to Two isolation valve on the same water pipe in the Bathrooms, Showers and Wetrooms area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
113
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
442
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
186
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock