[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]This is training for CPA1[/FONT][/FONT]
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman][/FONT][/FONT]
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]Carrying out a room test for carbon monoxide with a Combustion Analyser. [/FONT][/FONT]
[FONT=Times New Roman,Times New Roman]
[FONT=Times New Roman,Times New Roman]General [/FONT]
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]1. Position an open ended sampling probe approximately 2 m above floor level in the centre of the room and at least 1 m away from any suspect appliance installation. [/FONT]
[FONT=Times New Roman,Times New Roman]2. Close all external doors, windows and customer adjustable ventilation. [/FONT]
[FONT=Times New Roman,Times New Roman]3. Record the level of CO over a 15 min period. If the indoor level of CO starts to rise during this period, check for CO migration from other sources. [/FONT]
[FONT=Times New Roman,Times New Roman]4. If there is no rise then proceed to test the appliance. [/FONT]
[/FONT]Room sealed and open flued appliances
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]Operate the appliance at full rate until the CO reading stabilizes or begins to fall, whichever occurs first. [/FONT][/FONT]
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]Cookers [/FONT][/FONT]
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]Ensure that all permanent ventilation to the space in which the appliance is situated is unobstructed. [/FONT]
[FONT=Times New Roman,Times New Roman]Place a saucepan on each of the pan-supports above the two largest hotplate burners and put approximately a litre of water in each and cover with a lid. Use a saucepan with a flat base and a base diameter of between 160 mm and 220 mm. [/FONT]
[FONT=Times New Roman,Times New Roman]Place the grill pan in its highest position under the grill. [/FONT]
[FONT=Times New Roman,Times New Roman]Open/operate the customer adjustable ventilation in accordance with the cooker manufacturer’s instructions, e.g. window or extractor fan. [/FONT]
[FONT=Times New Roman,Times New Roman]Light the grill, oven and the two hotplate burners at their maximum setting. Turn the oven down to gas mark 5 (or mid-range if not calibrated in gas mark numbers). [/FONT]
[FONT=Times New Roman,Times New Roman]Record the CO levels at 1 min intervals. [/FONT]
[FONT=Times New Roman,Times New Roman]Turn the hotplate burners down to simmer when the water boils. Turn the grill off after 30 min. [/FONT]
[/FONT]If during the test the CO reading:
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]begins to fall without exceeding 30 ppm, stop the test; the installation and cooker are satisfactory; [/FONT]
[FONT=Times New Roman,Times New Roman]does not exceed 30 ppm for longer than 20 min and begins to fall and does not exceed 90 ppm at any time, stop the test; the installation and cooker are satisfactory; [/FONT]
[FONT=Times New Roman,Times New Roman]Exceeds 90 ppm at any time, stop the test, ventilate the room, identify the cause, rectify and repeat the test. [/FONT][/FONT]
Flueless water heaters
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]Ensure that all permanent ventilation to the space in which the appliance is situated is unobstructed. [/FONT]
[FONT=Times New Roman,Times New Roman]Close all customer adjustable ventilation to the space in which the appliance is situated. [/FONT]
[FONT=Times New Roman,Times New Roman]Light the appliance and operate it at maximum gas rate for 5 min recording the CO levels at 1 min intervals. [/FONT][/FONT]
Flueless space heaters
[FONT=Times New Roman,Times New Roman][FONT=Times New Roman,Times New Roman]Ensure that all permanent ventilation to the space in which the appliance is situated is unobstructed. [/FONT]
[FONT=Times New Roman,Times New Roman]Close all customer adjustable ventilation to the space in which the appliance is situated. [/FONT]
[FONT=Times New Roman,Times New Roman]Light the appliance and operate it at maximum gas rate for 30 min recording the CO levels at 1 min intervals. [/FONT][/FONT]
gb-gas
[/FONT][/FONT]