B

billybongo

I am looking at a megaflow that runs out of hot water quicker than it was .
I have megad both immersion heaters / stats and they read 19 ohms which is correct.
They both have a 230v supply . so i am confused as by all accounts they are ok.
Age of cylinder approx 7 years , thanks for any thoughts . Mark:confused:
 
Could be lime scale arround elements if in hard water area

Eco
 
oops hit post before I finished typing,
swap the stats over - sounds like top immersion & stat is working fine and giving about 1/3 of the hot water you usually get.
Bottom stat could be iffy?
 
Thanks for replies , we are in a hard water area but it has an electronic descaler on the feed , thats not to say it could be furred up.
Will try stat swop and if push comes to shove will take them out to look at them . cheers mark
 
Status
Not open for further replies.

Reply to Megaflow , a bit confused in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
135
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
472
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock