Discuss Glow worm ultimate problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

Paulus

Plumbers Arms member
Plumber
Messages
1,090
Hi

Just popped across from plumbing forum. I don't touch boilers as I am not gas safe and wouldn't know where to start anyway.

Before I get someone out to the above boiler I just wondered if you could help with a diagnosis. My radiators are getting incredibly hot even when I turn the boiler stat down to minimum but my water doesn't get as hot as it should.

If I turn the pump speed up the water temperature is much better but the rads are still red hot, too hot to touch even on minimum.

My first thought was the boiler stat.

Any guidance would be greatly appreciated.
 
I would agree boiler stat, disconnect electrically (the stat) to prove for certain
 
If it's getting over hot on the rads, you probably need a new boiler stat,but if you've turned the pump up & the dhw is hotter, my 1st thoughts are the circ's sludged/blocked.
With the Ultimate you can have a fully pumped or gravity circ's to the cylinder, if the later the cold feed & expansion will be connected at the cylinder F & Return. Get a magnet, put it on the tee that connects the cold feed, [could be blocking up.] if you feel the magnet holding you'll need to flush the system with chemicals or cut out all the effected pipework.
 
Many thanks to both of you. It is a fully pumped system. I flushed with chemicals before the winter but it obviously didn't work properly as you are dead right aggis, a magnet indicates sludge in pipes around the pump. I will try to flush again before resorting to replacing the pipes.
 
Hi Paulus - I know this is an old post, I've just come across it. I too have an old Glow Worm Ultimate with an identical problem, Rads getting red-hot. Have changed the boiler stat with no luck. Can you tell me how you sorted it out, was it successful ?
Would appreciate your comments. Ian
 
Hi Paulus - I know this is an old post, I've just come across it. I too have an old Glow Worm Ultimate with an identical problem, Rads getting red-hot. Have changed the boiler stat with no luck. Can you tell me how you sorted it out, was it successful ?
Would appreciate your comments. Ian

I emptied system again and re-filled adding Sentinel 400x. Left it in system for a couple of weeks and then flushed out and re-filled adding inhibiter. It seems to have worked but this winter will tell me for sure.
 
hear a lot of this, there should be nigh on 80 degrees at a rad, i wouldnt adjust anything at the chb. as long as you have an 11 degree diff over the flow/return all is well
 
Status
Not open for further replies.

Reply to Glow worm ultimate problem in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi I have a Glow-worm back boiler which is giving me grief (I would have upgraded it by now but its a listed building and there's issues with...
Replies
6
Views
538
Can anyone tell me of a boiler equivalent to a Glow worm micron 30ff. I am not sure what one I should get?
Replies
5
Views
717
The flue for a glow worm micron 30ff is apparently obsolete but there must be other flues that would fit it surely, it's just a standard 100mm...
Replies
7
Views
647
A
Good morning. We have a 10 year old Ultracom which now very frequently thinks there's a demand for hot water, even though there isn't, so the...
Replies
2
Views
910
Andy Don
A
I am looking for some basic advice please My house is on two floors, approx 240m2 and a spacious loft with good headroom and access. Glow Worm...
Replies
4
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock