does any one know the acceptable cpa levels for a boiler. I've just done a course at gas logic and the book that I got from them says if the ratio of co/co2 is above 0.008 then this should be investigated as it is not burning as it should.

fairly simple stuff but I had a boiler today which gave a reading of 0.0042 which I thought was fine.

however the engineer who i was working with said anything 0.004 or above needs a service???
my book says nothing about this???

also, does anyone have a view on the viper gas books as the book i have seems to omit vital info like discussed above.

thanks
 
Hi all

does any one know the acceptable cpa levels for a boiler. I've just done a course at gas logic and the book that I got from them says if the ratio of co/co2 is above 0.008 then this should be investigated as it is not burning as it should.

fairly simple stuff but I had a boiler today which gave a reading of 0.0042 which I thought was fine.

however the engineer who i was working with said anything 0.004 or above needs a service???
my book says nothing about this???

also, does anyone have a view on the viper gas books as the book i have seems to omit vital info like discussed above.

thanks

0.0042 is fine
 
you could do it to see it improves its , but theres no rule says you have to . we do a before and after reading
 
0.0042 is fine

Just worth noting that some manufacturers have a more stringent criteria for the ratio. Additionally, they may ask you to look at min/max CO[SUB]2[/SUB]%.

It's also worth looking at TB 126.
 
as general guide the action levels for boilers are- 0.004 before a service & 0.008 after a service but heres a question specifically for you lordyjordy111, why are you allowed a higher ratio ie 0.008 after servicing/cleaning.
 
TB stands for technical bulletin. They are produced by Gas Safe.

In this case, the TB recommends that boilers with air/gas ratio valves do not exceed a ratio .004 and if they do, they are considered AR. If exceeding .008, then ID.

But again, this is subject to MI. For instance Worcester Bosch Ri, are looking for a ratio of no more then .002. Any thing exceeding that requires a service.
 
Status
Not open for further replies.

Reply to CPA Analysis - acceptable readings in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
289
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
228
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
501
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
162
Hi they used to say as a last resort you could discharge the D2 pipework at high level and turn it back to the wall. Similar to a combi boiler. I have just looked back through the regs this seems to have changed and it isn't mentioned now. It now mentions if at high level it should be discharged...
Replies
11
Views
291
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock