Hi guys I'm a sweep and solid fuel fitter and I found this thread while googling for something else.
I was happy to see it because as a sweep I come across this problem regularly.
Gas fitter installs DFE fire and doesn't get the flue swept before fitting. After a few days of drying out the flue starts dropping soot all over their nice new install.
Not only is this a mess but soot is a highly toxic and acidic carcinogen. Let alone the fact that the flue hasn't been checked out.
Legal requirement or not surely common sense says get it swept first.
A pro sweep is trained and can issue safety certs that comply with all the regs and insurance requirement. This covers the installer back and reassures the customer.
Simply doing a spillage test is not enough.
On a job recently I found a blockage, its not unusual as midfeather bricks and parging mat'l can fall off and partially block the flue at the bends but this felt different. So I ran the cctv camera up and found 2 cans of Stella.
Turns out that the roofers they had used were hiding the beers in the pot, I guess the bag broke and the cans got lodged in the first bend.
The going rate for a sweep is about ÂŁ45.00 just add it to the bill. But use a pro sweep that can issue certs, these will be members of NACS, APICS, Guild of master chimney sweeps or The Institute of Chimney Sweeps.
I soundness test a lot of flues and I would say that getting on for 90% of the Victorian ones fail. It's usually the midfeathers, the brick walls that divide up the chimney into flues. These are just bricks stacked up on top of each other and not tied in at all and creates a continues vertical mortar seam on the breast and back wall. As time as gone by the motar falls out of this joint and allows the gasses to pass into the adjoining flue. The gases then hit the colder air and drop down the flue and come out of the other fireplace or vent bringing with it our old friend Carbon monoxide. Nice!
The other thing I see regularly is to do with the wrong terminals. I literally have a garage full of vent inserts that I've pulled out of pots. Vent inserts should not be left in if the flue is live, that goes for gas, oil or solid fuel.
For those that might be interested, here is a link to a list of terminals that must
not be used on any live flue.
http://www.apics.org.uk/images/WARNING_Do_not_use_these_Terminals_on_live_chimneys.pdf
Sorry if I've gone on a bit and am teaching grandmar to suck eggs but I see this all to often.
cheers
aZZaSweep