C

Christian

Hello, i have a baxi instant 105e and the pressure relief valve is letting water out of the external over flow pipe when ever the water pressure goes over 3bar.. i have had an external expansion tank fitted about a year ago. i have just fitted a new relief valve and within 10 minutes the pressure had risen to 3.5 and there is now a very fast drip out of over flow pipe. what is causing the pressure to rise in the boiler to cause the pressure relief vave to blow ?? pease help !!
 
1. Could be that new external tank wants recharging.
2. Filling loop is letting by
3. Pin hole in domestic heat exchanger.
 
is your filling loop connected? if it is then make sure isolating valve is turned off and disconnect one end off filling loop. then you no it cant be letting by and filling system.
 
Thank you for that, pipe is letting water through so i have just brought a new one, expansion vessel is at 2 bar
 
between 1bar and 1.5bar. forgot to mention filling loop should not be left connected only connect when system needs topping up.cheers grant.
 
The boiler is now working great thanks everyone who helped, isoating valve was stuck half open and and siezed soid. my vessel pressure is correct now aswell. :clap:
 
Status
Not open for further replies.

Reply to Baxi instant 105e combi pressure to high in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
118
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
195
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
127
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
244
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock