Both sides of the AAV got red hot??

OK' it looks as if it did, now can you set the AAV (temporarily) to index setting of 0.2 with boiler on, then stop the boiler and see if you are still getting that whooshing sound from the rad.
 
Last edited:
Both sides of the AAV got red hot??

OK' it looks as if it did, now can you set the AAV (temporarily) to index setting of 0.2 with boiler on, then stop the boiler and see if you are still getting that whooshing sound from the rad.
Thanks. Yes red hot. It only makes the crackling sound now and again. I can't make it do it so will have to test over a few days. Just for info when the boiler fired up the water loudly gushed around all the pipework for about 30 seconds or so.
 
Hi. Sorry for the late replies I did not get notifications. The boiler is downstairs under the stairs directly below the airing cupboard. The pump is in the boiler I don't have one seperatesl as far as I know
From what I’m gathering from your info the flow is on the right hand of the pic and the zone valve is on the return. If this is the case then B has to go to the boiler for it to work the way it’s been piped.
 
Thanks. Yes red hot. It only makes the crackling sound now and again. I can't make it do it so will have to test over a few days. Just for info when the boiler fired up the water loudly gushed around all the pipework for about 30 seconds or so.
Gushing sound; sounds like air in the system.
 
Gushing sound; sounds like air in the system.
There's nothing coming out of the rads when I bleed apart the from the towel rail that needs bleeding every week or so because the toprails don't get as warm. Lots of air comes out when I do that which is strange for a sealed system. Been doing it for over a year.
 
There's nothing coming out of the rads when I bleed apart the from the towel rail that needs bleeding every week or so because the toprails don't get as warm. Lots of air comes out when I do that which is strange for a sealed system. Been doing it for over a year.
If the towel rail constantly needs bleeding and nothing else does then it could be an issue with the towel rail which is quite common
 
Is there a AAV (automatic air vent) or a number of them in your system, if there is just check if the little cap on the air nozzle(s) on top of the AAV is open or shut, some prefer just to open these occasionally just to check for any air once all the air has been expelled after a drain down/refill of the system.

What pump/model have you got and what setting is it on?.
 
Is there a AAV (automatic air vent) or a number of them in your system, if there is just check if the little cap on the air nozzle(s) on top of the AAV is open or shut, some prefer just to open these occasionally just to check for any air once all the air has been expelled after a drain down/refill of the system.

What pump/model have you got and what setting is it on?.
Hi. No aavs on system. The only pump I have is inside the boiler as far as I know. Is that right for an unvented system?
 
That's correct (gas boiler) and you can't access it (not GSR) , post #57 above suggests that it could be a issue with the towel rail.

I meant to ask you this before, why did you decide to fit a ABV??, was it because the boiler manufacturers require it or some other reason.
 
That's correct (gas boiler) and you can't access it (not GSR) , post #57 above suggests that it could be a issue with the towel rail.

I meant to ask you this before, why did you decide to fit a ABV??, was it because the boiler manufacturers require it or some other reason.
Yes the boiler recommend it even when there is one built in. This is if all there wasn't a bypass rad. Also since the unvented system was fitted the radiators make a loud hissing noise so the installer recommended he try this to see if it helps. Since the bypass was fitted and inhibitor put in it is now have hissing and crackling. Wish I didn't bother to upgrade now. Cost me over £6k
 
You would think the installer should sort it out if these problems are there from the time of the upgrade but you probably know all this, I'm afraid I can't offer you any other suggestions.
 
Hi. No aavs on system. The only pump I have is inside the boiler as far as I know. Is that right for an unvented system?
The boiler probably has one, there should certainly be at least one more installed in the system, this is often on a T piece where the cylinder coil enters the cylinder top and before any MV.
 
I have a feeling that the ABV when opening is allowing trapped air in your system into the return and causing all sorts of issues (not the ABVs fault) , if a AAV or manual air release isn't fitted then how was the air in the system initially released on refilling the system I wonder, the boiler AAV is fitted to remove air from the boiler and not the system but may do so over a prolonged period but I wouldn't bet on it.
One other query, if there is a pressure gauge in the boiler display, it should read ~ 1bar when cold and ~ 1.5 to 2.0 bar hot.
 
I have a feeling that the ABV when opening is allowing trapped air in your system into the return and causing all sorts of issues (not the ABVs fault) , if a AAV or manual air release isn't fitted then how was the air in the system initially released on refilling the system I wonder, the boiler AAV is fitted to remove air from the boiler and not the system but may do so over a prolonged period but I wouldn't bet on it.
One other query, if there is a pressure gauge in the boiler display, it should read ~ 1bar when cold and ~ 1.5 to 2.o bar hot.
Had a look and can’t see one on any pipework. Yes pressure is fine under 2 when hot and a tiny bit over 1 when cold.

I think the air got in when refilling and wasn’t released.
 
He’s been installing for over 30 years. Surely he would have put one there?
He’s been installing for over 30 years. Surely he would have put one there?
Can't answer that one, is he aware that you are still having problems after the fitting of the ABV?, if not just pick up the phone and ask him to return and sort things out, your system never seems to have been right since the upgrade.
 
OK then, there must be plenty of good plumbers in your area, I'm sure there is some way on here that you can privately (conversation?) ask one of the many professionals on here if they could recommend one near you.
 

Reply to Automatic Bypass Valve Query in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have a heating system comprised of skirting radiators that form part of a loop from the boiler, round the house and back. Some rooms get...
Replies
1
Views
183
  • Question
A plumber recently told me my bypass pipework is poorly designed as it’s offering a low path of resistance v the motorised valve T junctions, and...
Replies
17
Views
2K
Do people with this type of mixed flow temperature control have any problems with achieving the required manifold flow temperature? The one below...
Replies
3
Views
739
Hi All Bit of an urgent one being that time of year and can't get a plumber out until after xmas even on an emergency callout I have just...
Replies
2
Views
355
    • Like
Hello, my Mothers heating failed in the recent UK cold snap. I found the pump was stuck. I have a question about pump orientation. The...
Replies
8
Views
700
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock