Is there a hw off wire from the programmer to the wiring ctr ?If there isn't it could have been wired up for hw to be permamently live to make the customer think htg works on its own.

yes there was hw off on programmer
 
Was it a Grudfoss UPS 2 you fitted by any chance? What make is the timer?

pump was as you say new grundfoss a rated and programmer iflo twin channel. electrician re wired junction box 3 times I think something is back feeding through the programmer but no idea how :-(
 
I had exactly the same issue the other week. I got though quite a few programmers as thought it was an issue with a batch of programmers. Turns out its an issue with the new Grundfos UPS 2.
Apparently according to Drayton tech support its a know issue. When the pump starts for some reason it draws a abnormally high current which causes the relays in the timer to fuse. Once this happens it is the end of your brand mew timer.
You can check the timer has fused by removing it from the back plate and doing a continuity check on the back of the timer between L and 3 or 4. They should be open circuit when removed.
The Drayton guy said they know it affects Drayton (iflo) and Danfoss timers, but were unaware of issues with other manufacturers. Draytons resolution was fit a Grundfos Alpha or a different brand pump.
Grundfos will not openly admit there is a fault however have a new version of the pump coming in September to address this issue. Hope this helps.
 
I had exactly the same issue the other week. I got though quite a few programmers as thought it was an issue with a batch of programmers. Turns out its an issue with the new Grundfos UPS 2.
Apparently according to Drayton tech support its a know issue. When the pump starts for some reason it draws a abnormally high current which causes the relays in the timer to fuse. Once this happens it is the end of your brand mew timer.
You can check the timer has fused by removing it from the back plate and doing a continuity check on the back of the timer between L and 3 or 4. They should be open circuit when removed.
The Drayton guy said they know it affects Drayton (iflo) and Danfoss timers, but were unaware of issues with other manufacturers. Draytons resolution was fit a Grundfos Alpha or a different brand pump.
Grundfos will not openly admit there is a fault however have a new version of the pump coming in September to address this issue. Hope this helps.
This is a really helpful comment.:cool4:
 
It's only the UPS 2 causing the issue. No other pumps. I would suggest either fitting a Grundfos Alpha or a different brand. I did this and I had no issues. The likely hood is that it is probably affecting all timers that incorporate electronic relays. Don't think I would bother trying to find out which timers do and don't work with it, could get quite costly.
 
Sounds like a problem I had a few weeks ago. There was around 130v on the heating on wire coming from the mid pos valve head, even when disconnected from the wiring centre! If I nudged the valve lever with no demand it jumped over to heat on.

Checked over the wiring, all fine except for this 130 or so volts. Swapped the valve head which made no difference. In the end I fitted a different valve, can't remember if it was Hwell to Drayton or the other way around but it now works! I double checked the wiring which seemed fine and no call back.
 
I had exactly the same issue the other week. I got though quite a few programmers as thought it was an issue with a batch of programmers. Turns out its an issue with the new Grundfos UPS 2.
Apparently according to Drayton tech support its a know issue. When the pump starts for some reason it draws a abnormally high current which causes the relays in the timer to fuse. Once this happens it is the end of your brand mew timer.
You can check the timer has fused by removing it from the back plate and doing a continuity check on the back of the timer between L and 3 or 4. They should be open circuit when removed.
The Drayton guy said they know it affects Drayton (iflo) and Danfoss timers, but were unaware of issues with other manufacturers. Draytons resolution was fit a Grundfos Alpha or a different brand pump.
Grundfos will not openly admit there is a fault however have a new version of the pump coming in September to address this issue. Hope this helps.

thanks for this post its realy helped I thought I was going mad - this job realy got to me this wk - thought about going to work in Tesco no stress
 
Status
Not open for further replies.

Reply to another of those days on a y plan in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello. I've just replaced our old Potterton EP2 CH controller with a Drayton Wiser HubR (& peripherals). The old backing plate wasn't...
Replies
1
Views
294
Customer complains of Intermittent heating on Y plan with Stat satisfied. New boiler fitted last year (no permanent live required or fitted...
Replies
25
Views
2K
Hi all, so things are coming on now at last! New 250 cylinder in loft all pretty much plumbed in. F+E tank binned off, new ups pump, 2 new zone...
Replies
58
Views
3K
Customer complained of hot water tank getting hot when no demand Y plan system couldn't see any issues so I watched it Timer set to CH only, HW...
Replies
13
Views
2K
Hi, I'm brand new to plumbing, heating systems, wiring etc and only started to read about it because I wanted to know why our CH would only work...
Replies
1
Views
820
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock