called to a job today no htg or hw. find fuse in board blown and 13amp fuse in spur.trace to pump fault - replace pump with a rated all merchants now stock at £110 . all good but notice with programmer off the boiler and pump on running through bypass. remove htg on wire from junction box and its live find pump failing has welded contact in programmer closed . call sparky as I have busy day and call back later to see him . we replace programmer and still the same so I exchange for another programmer and now it works on htg but hw on wire is live with programmer off . we remove orange and white wires from junction box to zone valve and switch back on to find zone valve powers to htg position now we are puzzled.i get new Honeywell head and fit and now htg works fine and room stat but now hw on wire is constantly live . we put hw on zone valve stays in hw only , then I put htg on and zone valve moves to mid position then I turn cyl stat down and zone valve moves fully to htg only so its working as it should but turn htg and hw off and hw on wire is still live until hw is satisfied . sparky puzzled now and leave at that for now are there any sparkys that can shed some light this job has stressed me out.thanks ant
 
Agree with you there. Forget what's there, trace your wiring and go back to the original Y plan wiring diagram. I take it you have a ten way junction box. Tip I always use to cut down the confusion, all the green/yellows in one terminal, all the blues in another, that leaves you with only a few to think about.
 
Agree with you there. Forget what's there, trace your wiring and go back to the original Y plan wiring diagram. I take it you have a ten way junction box. Tip I always use to cut down the confusion, all the green/yellows in one terminal, all the blues in another, that leaves you with only a few to think about.
that was my next plan to return with 10 way box and cyl stat - I just thought sparky would sort as I didn't have time to get involved but ended up having to
 
Sparkies generally don't understand heating system wiring, especially 'Y' plan.
 
Is there a hw off wire from the programmer to the wiring ctr ?If there isn't it could have been wired up for hw to be permamently live to make the customer think htg works on its own.
 
i had one last week the pump was wired to the heating on the clock and there was no pump on hot water only boiler going to overheat cylinder stat fell to bit as soon as i touched it ,allegedly wired by BG
 
Was it a Grudfoss UPS 2 you fitted by any chance? What make is the timer?
 
Is there a hw off wire from the programmer to the wiring ctr ?If there isn't it could have been wired up for hw to be permamently live to make the customer think htg works on its own.

yes there was hw off on programmer
 
Was it a Grudfoss UPS 2 you fitted by any chance? What make is the timer?

pump was as you say new grundfoss a rated and programmer iflo twin channel. electrician re wired junction box 3 times I think something is back feeding through the programmer but no idea how :-(
 
I had exactly the same issue the other week. I got though quite a few programmers as thought it was an issue with a batch of programmers. Turns out its an issue with the new Grundfos UPS 2.
Apparently according to Drayton tech support its a know issue. When the pump starts for some reason it draws a abnormally high current which causes the relays in the timer to fuse. Once this happens it is the end of your brand mew timer.
You can check the timer has fused by removing it from the back plate and doing a continuity check on the back of the timer between L and 3 or 4. They should be open circuit when removed.
The Drayton guy said they know it affects Drayton (iflo) and Danfoss timers, but were unaware of issues with other manufacturers. Draytons resolution was fit a Grundfos Alpha or a different brand pump.
Grundfos will not openly admit there is a fault however have a new version of the pump coming in September to address this issue. Hope this helps.
 
I had exactly the same issue the other week. I got though quite a few programmers as thought it was an issue with a batch of programmers. Turns out its an issue with the new Grundfos UPS 2.
Apparently according to Drayton tech support its a know issue. When the pump starts for some reason it draws a abnormally high current which causes the relays in the timer to fuse. Once this happens it is the end of your brand mew timer.
You can check the timer has fused by removing it from the back plate and doing a continuity check on the back of the timer between L and 3 or 4. They should be open circuit when removed.
The Drayton guy said they know it affects Drayton (iflo) and Danfoss timers, but were unaware of issues with other manufacturers. Draytons resolution was fit a Grundfos Alpha or a different brand pump.
Grundfos will not openly admit there is a fault however have a new version of the pump coming in September to address this issue. Hope this helps.
This is a really helpful comment.:cool4:
 
It's only the UPS 2 causing the issue. No other pumps. I would suggest either fitting a Grundfos Alpha or a different brand. I did this and I had no issues. The likely hood is that it is probably affecting all timers that incorporate electronic relays. Don't think I would bother trying to find out which timers do and don't work with it, could get quite costly.
 
Sounds like a problem I had a few weeks ago. There was around 130v on the heating on wire coming from the mid pos valve head, even when disconnected from the wiring centre! If I nudged the valve lever with no demand it jumped over to heat on.

Checked over the wiring, all fine except for this 130 or so volts. Swapped the valve head which made no difference. In the end I fitted a different valve, can't remember if it was Hwell to Drayton or the other way around but it now works! I double checked the wiring which seemed fine and no call back.
 
I had exactly the same issue the other week. I got though quite a few programmers as thought it was an issue with a batch of programmers. Turns out its an issue with the new Grundfos UPS 2.
Apparently according to Drayton tech support its a know issue. When the pump starts for some reason it draws a abnormally high current which causes the relays in the timer to fuse. Once this happens it is the end of your brand mew timer.
You can check the timer has fused by removing it from the back plate and doing a continuity check on the back of the timer between L and 3 or 4. They should be open circuit when removed.
The Drayton guy said they know it affects Drayton (iflo) and Danfoss timers, but were unaware of issues with other manufacturers. Draytons resolution was fit a Grundfos Alpha or a different brand pump.
Grundfos will not openly admit there is a fault however have a new version of the pump coming in September to address this issue. Hope this helps.

thanks for this post its realy helped I thought I was going mad - this job realy got to me this wk - thought about going to work in Tesco no stress
 
Status
Not open for further replies.

Reply to another of those days on a y plan in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
125
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
245
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...