Good morning all, Did a CP12 yesterday and got 26 mbar Standing & 21 mbar working pressures at the meter so all good, but then found 22 mbar on the cooker burner and also 22 mbar at the inlet of the boiler??? Never come across a higher pressure at the appliance than at the meter before, Checked it three times to make sure with my U gauge and my FGA. Anyone else come across this before? Thought it was a bit strange.
 
How can you have more pressure working at the appliance when you only have 21 at the meter ?

External gas run ?
 
Hi Shaun, yes HOW I don't know. But you may have just answered my query. The meter was in a brick compartment accessed from a small wooden door on the outside of the building under the concrete stairs and it was a cold shaded little compartment. Whereas the pipework ran in 22mm for 4m external along the wall with the sun shining on it.
 
There you go heat will rise it 3-4 mbar

Bet your working was around 20 mbar
 
Thanks Shaun, 35yrs in the game and still learning. It is the first time I have ever come across this before. Wonder how many other GSR folk have come across it?

A few and I bet they phoned transportation up saying help :D
 
I have had this quite alot you can cause a rise just by holding onto the gas supply i try and test early morning or late afternoon in the sunny weather. Kop
 
try putting a blow touch over the gas pipe when you send the apprentice to take a tightness test
 
Status
Not open for further replies.

Reply to Strange readings at the appliance... in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Non-professional / knowledgeable person here. I'm a Brit in Romania who volunteers for a charity building an old peoples home for needy old...
Replies
3
Views
411
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not...
Replies
1
Views
633
HI all, finished fitting the above boiler yesterday. Straight swap, side access flue with only the elbow off the boiler. Gas pressure 21mbars on...
Replies
2
Views
2K
Hi I've read through dozens of threads on here about unvented systems but was wondering if someone might provide some advice on an upgrade we...
Replies
26
Views
3K
I have a pdaily loss of pressure in a closed circuit system as noticed on the gauge at the filling point 2 bar to 0. After exhausting all the...
Replies
5
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock